I do not when I use an inside fire pump system for the water supply that does not supply the outside fire hydrants.
John John August Denhardt, P.E. Strickland Fire Protection Incorporated 5113 Berwyn Road College Park, Maryland 20740 Office Telephone Number: 301-474-1136 Mobile Telephone Number: 301-343-1457 FIRE SPRINKLERS SAVE LIVES -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Dewayne Martinez Sent: Tuesday, April 06, 2010 8:43 AM To: [email protected] Subject: Hose allowance I am calculating a new ESFR system that is supplied by an existing fire pump. I am using a recent fire pump test as my water supply information and calculating the system back to the pump discharge flange. My question is when picking up hose allowance, NFPA dictates 250GPM. Normally I would put 100gpm inside and 150gpm outside. Since I am calculating back to the pump discharge flange, do I still need to include the 150 outside house? If so, where? Thanks, Dewayne Martinez Design Build Fire Protection New Berlin, WI _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)