I would use 130 sq.ft.,simply because it is outside the dwelling unit and 
requires 13 design and because of the structure (even for light hazard).


---- Dewayne Martinez <[email protected]> wrote: 
> Thanks Tom,
> In this case the AHJ is letting us use LH.  Any thoughts on the 225 vs
> 130 spacing? 
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Tom
> Duross
> Sent: Friday, April 09, 2010 6:49 AM
> To: [email protected]
> Subject: RE: Unfinished basements in 4-family NFPA 13R occupancy
> 
> I use OH in residential basements, all steel and up through the floor,
> then transition to plastic above the floor. 
> Tom
> 
> 
> I have a 4-family 13R (07ed) building with unfinished basements.  Please
> confirm if my logic is on tract for sprinklering these areas.
> For most AHJ's here, basements are not considered part of the dwelling
> unit so they fall under section 6.8.2 - outside dwelling unit.
> Only the design discharge and design area criteria from 13 apply so I
> can sprinkler this area as LH with 225sf spacing no matter the type of
> construction.  IE: I don't have to reduce the head spacing to 130sf
> because of the TJI's 16" O.C.
> Sound ok?
> Thanks,
> Dewayne Martinez
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to