Dear all.. We are in the process of installing *temporary fire protection* for a 30 story builing. The pump installed is a *single diesel engine pump* (Not listed) for the supplying water for the landing valves in each floor.The fire pump is located in the basement floor and is barricaded .
The operation of the fire pump will be such that In case of pressure drop due to opening of the hosereeel or landing valves the pump will start. Now during the inspection from Client,they asked us why there is no automatic shutoff . *The scenario they are considering is *. Suppose some labour accidentally opens the hosreel for anypurpose,the pump will start running and if there is noone to stop the pump ,will it get damaged.? I suggested we could provide a fire alarm bell for alerting the people. *Can we provide automatic shuttoff for the diesel pump. Is it acceptable as per NFPA?* Is there anyother options available or anything from NFPA to support that we dont need automatic shutoff? Please give your valuable inputs. Sam _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)