Sam,

I don't mean to be a smart ass but follow along. You have a special
circumstance you're trying to mitigate against. Your route is to
automatically do something that is typically disallowed without
special dispensation. His greatness, the Dead One has suggested a
different tack which is essentially Biblical in scope: Render unto
NFPA what is NFPA's and unto the problem that which is the Problem's.
If you owned an airline the planes will have seats for pilot and
co-pilot. There is an expectation on the part of the manufacturer, the
regulator, and, unconsciously, the customer that both seats will be
filled. You don't get to put crash test dummies in the seats, or some
other alternative,  because you don't have a real pilot. You find
another solution. If you're required to have manual shut-down, and
there's a fear of inadvertent start-up leading to continuous run until
the pump self destructs then the OWNER will need to assure that a
qualified person is on site that can monitor and operate the pump, or
that, as Bob suggests, a pump run notification device be attached
(you'll also need a trained person on site that knows what that means
and has a procedure to deal with it: call the service company, shut it
down properly, whatever he's trained to do), or some other procedure
that allows the pump to run the required time and is then manually
shut down.

On Mon, Apr 12, 2010 at 6:19 AM, Bob Caputo <[email protected]> wrote:
> While pumps are intended to start automatically (on a pressure drop) it is
> intended that upon receipt of alarm indicating the pump is running, a
> qualified person will be dispatched to the pump room to monitor conditions
> and provide shut down after 30 minutes if the pump isn't actually needed.
> This is especially true of electric motor drive pumps because it's not good
> for the motor to start and stop without allowing it to run at least 10
> minutes.
>
> Even your temporary water supply pump should have a running alarm to some
> central station, job shack or similar but again, non-listed pumps are not
> the subject of NFPA 20 so do whatever your local AHJ requires
>
> <insert stand disclaimer here>
>
> bc
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of sam b
> Sent: Monday, April 12, 2010 12:36 AM
> To: [email protected]
> Subject: Re: FIRE PUMP: Urgent
>
> Thaanx bob
>
> I just went through the same now.
>
> But If am not providing an automatic shutoff facility,how can I avoid  any
> damage to the pump in case of mentioned scenario
> >From the pump supplier I cant expect anything .so from our side what we can
> do to make it more safe.?
>
> any thoughts?
>
>
> Regards
>
> Sam
>
>
>
> On Mon, Apr 12, 2010 at 10:44 AM, Bob Caputo <[email protected]> wrote:
>
>> Since your pump is not listed, you don't comply with NFPA 20 so why does
> it
>> matter if the standard allows an automatic shut off?   For your use, the
>> 2010 edition of NFPA states the following:
>>
>>
>>
>> 12.7.2.6 Sole Supply Pumps.
>>
>> 12.7.2.6.1 Shutdown shall be accomplished by manual or automatic means.
>>
>> 12.7.2.6.2 Automatic shutdown shall not be permitted where the pump
>> constitutes the sole source of supply of a fire sprinkler or standpipe
>> system or where the authority having jurisdiction
>>
>> has required manual shutdown.
>>
>>
>>
>> Regardless of the pump listing or other compliance issues, the answer lies
>> solely with the permission of the local AHJ.
>>
>> Important Notice: As a member of the NFPA 13 Installation & NFPA 25
>> Committee's, this correspondence is not a Formal Interpretation issued
>> pursuant to NFPA Regulations. Any opinion expressed is the personal
> opinion
>> of the author, and does not necessarily represent the official position of
>> the NFPA or its Technical Committees. In addition, this correspondence is
>> neither intended, nor should be relied upon, to provide consultation or
>> services.
>>
>> Bob Caputo
>>
>>
>>
>>
>>
>>
>>
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of sam b
>> Sent: Sunday, April 11, 2010 11:15 PM
>> To: [email protected]
>> Subject: FIRE PUMP: Urgent
>>
>>
>>
>> Dear all..
>>
>>
>>
>> We are in the process of installing *temporary fire protection* for a 30
>>
>> story builing.
>>
>> The pump installed is a *single diesel engine pump* (Not listed) for the
>>
>> supplying water for the landing valves in each floor.The fire pump is
>>
>> located in the basement floor and is barricaded .
>>
>>
>>
>> The operation of the fire pump will be such that In case of pressure drop
>>
>> due to opening of the hosereeel or landing valves the pump will start.
>>
>> Now during the inspection from Client,they asked us why there is no
>>
>> automatic shutoff .
>>
>> *The scenario they are considering is *.
>>
>> Suppose some labour accidentally opens the hosreel for anypurpose,the pump
>>
>> will start running and if there is noone to stop the pump ,will it get
>>
>> damaged.?
>>
>> I suggested we could provide a fire alarm bell for alerting the people.
>>
>> *Can we provide automatic shuttoff for the diesel pump. Is it acceptable
> as
>>
>> per NFPA?*
>>
>> Is there anyother options available or anything from NFPA to support that
>> we
>>
>> dont need automatic shutoff?
>>
>>
>>
>> Please give your valuable inputs.
>>
>>
>>
>> Sam
>>
>> _______________________________________________
>>
>> Sprinklerforum mailing list
>>
>> [email protected]
>>
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>>
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>>
>>
>> To Unsubscribe, send an email
> to:[email protected]<to%3asprinklerforum-requ...@fire
> sprinkler.org>
>>
>> (Put the word unsubscribe in the subject field)
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email
> to:[email protected]<to%3asprinklerforum-requ...@fire
> sprinkler.org>
>> (Put the word unsubscribe in the subject field)
>>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA, NIBS, WSAFM, WFC
_______________________________________________