Grating is grating.  It deflects and is an obstruction to the sprinkler spray 
pattern.  Heads need to be below.

Open grid ceilings are a different animal as they typically occur moreso in 
light or possibly ordinary hazard occupancies. 

Ceilings are one thing and floor grating is another.  Don't confuse the two.

If you have 2007, look at 8.5.5.3.3 and A.8.5.5.3.

8.5.5.3.3* Sprinklers installed under open gratings shall be of the 
intermediate level/rack
storage type or otherwise shielded from the discharge of overhead sprinklers.

Commentary:

 FAQ:Where open grating is utilized, are additional sprinklers required below 
the open grating? 

Sprinklers installed under open gratings are addressed in 8.5.5.3.3. Although 
open grating 
allows heat from a fire to pass through it and reach a sprinkler, the openings 
are not adequate 
to compensate for obstructions to the sprinkler spray pattern. Thus, 
supplemental sprinklers 
under the open grating deck are necessary. Gratings or slatted decks and 
walkways are
frequently covered with goods in storage or by a light surface dust stop. 
Sprinklers are
required under such gratings and walkways. Sprinklers located below the open 
grating must
be provided with a water shield or be of the intermediate level/rack storage 
type to prevent
water from sprinklers that are operating above from wetting the thermal element 
and delaying
sprinkler operation.


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of George Medina Jr
Sent: Tuesday, April 13, 2010 7:06 PM
To: [email protected]
Subject: Grating

What is the dimensions of grating when sprinklers are required underneath? I 
looked under NFPA-13 (2007 ed.) index for Grating and found no specifications.
.

George Medina Jr. 

=
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to