Boxes are placed on grated floors, creating obstructions to spray that
aren't apparent at final inspection.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Wednesday, April 14, 2010 8:29 AM
To: [email protected]
Subject: RE: Grating

Grating is grating.  It deflects and is an obstruction to the sprinkler
spray pattern.  Heads need to be below.

Open grid ceilings are a different animal as they typically occur moreso in
light or possibly ordinary hazard occupancies. 

Ceilings are one thing and floor grating is another.  Don't confuse the two.

If you have 2007, look at 8.5.5.3.3 and A.8.5.5.3.

8.5.5.3.3* Sprinklers installed under open gratings shall be of the
intermediate level/rack
storage type or otherwise shielded from the discharge of overhead
sprinklers.

Commentary:

 FAQ:Where open grating is utilized, are additional sprinklers required
below the open grating? 

Sprinklers installed under open gratings are addressed in 8.5.5.3.3.
Although open grating 
allows heat from a fire to pass through it and reach a sprinkler, the
openings are not adequate 
to compensate for obstructions to the sprinkler spray pattern. Thus,
supplemental sprinklers 
under the open grating deck are necessary. Gratings or slatted decks and
walkways are
frequently covered with goods in storage or by a light surface dust stop.
Sprinklers are
required under such gratings and walkways. Sprinklers located below the open
grating must
be provided with a water shield or be of the intermediate level/rack storage
type to prevent
water from sprinklers that are operating above from wetting the thermal
element and delaying
sprinkler operation.


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George Medina
Jr
Sent: Tuesday, April 13, 2010 7:06 PM
To: [email protected]
Subject: Grating

What is the dimensions of grating when sprinklers are required underneath? I
looked under NFPA-13 (2007 ed.) index for Grating and found no
specifications.
.

George Medina Jr. 

=
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to