Hey Chris, where you say "Bad idea, against the law (NFPA 13) and not worth the 
risk."

Are you saying insulating pipe is against the law per 13?

If so how do you interpret 8.16.4.1.3 "Where aboveground water-filled supply 
pipes, risers, system risers, or feed mains pass through open areas, cold 
rooms, passageways, or other areas exposed to temperatures below 40°F (4°C), 
the pipe shall be protected against freezing by insulating coverings,  
frostproof casings, listed heat tracing systems, or other reliable means 
capable of maintaining a minimum temperature between 40°F (4°C) and 120°F 
(48.9°C).",  specifically the terms "insulating coverings or frostproof 
casings"?



Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Chris Cahill
Sent: Thursday, April 15, 2010 9:23 AM
To: [email protected]
Subject: RE: Pipe Wrapping

Well yes but.  Insulation of non-flowing fluids in a pipe such as our systems 
will be aided by insulation but not in the way the insurance guy suggested.  
The insulation will slow the heat loss.  So if I have two identical wet 
sprinkler pipes, one with insulation, one without, running through a cold space 
at say 65 deg F in the afternoon and the temp drops at night to say 20 deg F 
the one without the insulation will freeze first.  The difference in time can 
be calculated.  

And as the local temperature changes in the pipe convective currents can set up 
transferring some cold liquid to a warmer space and some of the warmer space 
fluid returning to the cold side. This will further slow freezing but might be 
harder to quantify. And I'd suspect the insulation would help here
too.   

If you live in an area that might see sub freezing for only a couple hours 
enough insulation MIGHT prevent a freeze where a short uninsulated pipe would 
freeze.

Now I'm discussing the details of insulation not the wisdom of using it on 
sprinkler pipe without heat tracing or some other heat source.  Bad idea, 
against the law (NFPA 13) and not worth the risk.

But hey if the owner tells you to go this way or the insurance guy get it in 
writing and at least you will have regular service work without liability
for freezing.        

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Thursday, April 15, 2010 7:30 AM
To: [email protected]
Subject: RE: Pipe Wrapping

Insulating piping to prevent freezing or to maintain fluid temps in various 
conditions is a mechanical engineering function and is done all the time, no 
black magic there, just numbers.  It's a matter of simple heat loss 
calculations that can determine the amount of insulation needed to minimize the 
heat loss of the fluid within the pipe.  If you know the water temp in the pipe 
is for instance 50 degrees and the ambient temp could be say 30 degrees, you 
can calculate the R-value of the insulation based on the data.
It's all pretty basic stuff dealing with conductance, transference and 
resistance.  But if someone is just going to the Big Box home improvement store 
and buying a few sticks of 1/2" slip-on foam insulation, they have nothing to 
substantiate what that will achieve without someone doing some calcs.  


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Jay Jay Blocker
Sent: Wednesday, April 14, 2010 9:43 PM
To: [email protected]
Subject: Re: Pipe Wrapping

I got a call from a manager of seven hotels.  Over the past five years they 
have had 600k in insurance claims due to frozen pipes.  One of the (so well
educated) investigators from the insurance company saw some wet pipe that runs 
within six feet of vents to the outside air.  The investigator said the pipe 
should be wrapped to prevent freezing.  I asked if the pipe is required to stay 
at 40 degrees how can the manufacture of the insulation (which would be bought 
at a big box store locally) could GUARANTEE the pipe will stay at or above that 
temperature. Point being that moving the pipe away from the vent or sealing the 
vent is a better option to reduce the risk of seeing such temperatures.
 
J
EFPS
(303) 353-9712




________________________________
From: Scott A. Futrell <[email protected]>
To: [email protected]
Sent: Tue, April 13, 2010 8:03:08 AM
Subject: RE: Pipe Wrapping

What is the context of your question?  Why would you want to wrap sprinkler 
pipe with pipe insulation?    You can't wrap it like domestic pipe in an 
unheated space, the water will most likely freeze anyway eventually. Moisture 
doesn't condense on the outside of it.  So what is the reason?

Scott Futrell

(763) 425-1001 Office
(612) 759-5556 Cell


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of John Denhardt
Sent: Monday, April 12, 2010 6:55 PM
To: [email protected]
Subject: RE: Pipe Wrapping

I believe you were dreaming.

John

John August Denhardt, P.E.
Strickland Fire Protection Incorporated
5113 Berwyn Road
College Park, Maryland 20740
Office Telephone Number:  301-474-1136
Mobile Telephone Number:  301-343-1457
FIRE SPRINKLERS SAVE LIVES 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Jay Jay Blocker
Sent: Monday, April 12, 2010 8:13 PM
To: [email protected]
Subject: Pipe Wrapping

I thought I once saw something saying that sprinkler pipe cant be wrapped 
with pipe insulation.  Am I dreaming or does this code exist?  I cant locate it.
 
J. Blocker
EFPS
(303) 353-9712


      
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)



      
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to