Because 'design approaches' addresses the amount of water--- 'calc
procedure' addresses the 'shape' of the application of that water

-----Original Message-----
From: Brad [mailto:[email protected]] 
Sent: Tuesday, April 20, 2010 2:56 PM
To: [email protected]; [email protected]
Subject: RE: Calc Area

I separated sliding along the curve from in 'design approaches' from 1.2
wording in 'calculation procedure' 

-----Original Message-----
From: Travis Mack, SET [mailto:[email protected]] 
Sent: Tuesday, April 20, 2010 2:48 PM
To: [email protected]; [email protected]
Subject: Re: Calc Area

Brad:

I think you would only have to re-evaluate your lengths if you modified 
your density.  If, because my head layout is irregular, my remote area 
turns out to be 1620 sq ft and I base my design criteria on 0.10/1500 
then I am fine with a minimum remote area length of 1.2*(1500^.5).  
However, if I interpolate my density to something such as 0.098 / 1640, 
then I am going to need to have 1.2*(1640)^.5.  This is the same as if I 
am required to do a 3000 sq ft calc.  I can reduce my density to 0.07 / 
3000, but my remote area length must be a minimum of 1.2*(3000^.5).

Am I missing something here?

On 4/20/2010 12:44 PM, Brad wrote:
> I was shocked when first confronted with the idea 8 years ago--- let us
see
> what others have to say...
>
> -----Original Message-----
> From: ParsleyConsulting [mailto:[email protected]]
> Sent: Tuesday, April 20, 2010 2:35 PM
> To: [email protected]
> Subject: Re: Calc Area
>
> Brad,
>
> I was intrigued by your remarks about having to re-evaluate the minimum
> length of the remote area parallel to the branch lines if you were to
> end up with a remote area of a different size than where the standard
> initially had you start.
>
> I can't find anything in my copy of the NFPA-13 handbook, or the
> Hydaulic Design text book by Pat Brock from Oklahoma State which even
> remotely suggests this is a requirement.
>
> I've never done this, and I want to be sure I haven't missed something
> critical.  I need to be sure I understand what you're saying, because
> for me the implications are huge for the plans I review on a daily basis
> for a number of AHJ's.
>
> Are you stating that if in order to meet the requirements for a 1,500
> square foot remote area I were to end up with a remote area of 1,600
> square feet I then have to make an evaluation to make sure that the
> length of the remote area parallel to the branch lines is at least 1.2 x
> sqrt of 1,600?  In effect, I need at least 48'-0", not the 46'-5" I
> started with?  If that's your position, can you give me some idea of how
> you determined that such an additional requirement is necessary?
>
> I've got to tell you that if that is truly the case, I'm in seriously
> deep trouble, as I've been doing calculations and plan reviews based on
> a flawed premise, and that makes me really nervous.
>
> Can you give me/us some background on how you came to that conclusion?
>
> I'd really appreciate the help.
>    

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to