Brad,

I was intrigued by your remarks about having to re-evaluate the minimum 
length of the remote area parallel to the branch lines if you were to 
end up with a remote area of a different size than where the standard 
initially had you start.

I can't find anything in my copy of the NFPA-13 handbook, or the 
Hydaulic Design text book by Pat Brock from Oklahoma State which even 
remotely suggests this is a requirement. 

I've never done this, and I want to be sure I haven't missed something 
critical.  I need to be sure I understand what you're saying, because 
for me the implications are huge for the plans I review on a daily basis 
for a number of AHJ's.

Are you stating that if in order to meet the requirements for a 1,500 
square foot remote area I were to end up with a remote area of 1,600 
square feet I then have to make an evaluation to make sure that the 
length of the remote area parallel to the branch lines is at least 1.2 x 
sqrt of 1,600?  In effect, I need at least 48'-0", not the 46'-5" I 
started with?  If that's your position, can you give me some idea of how 
you determined that such an additional requirement is necessary? 

I've got to tell you that if that is truly the case, I'm in seriously 
deep trouble, as I've been doing calculations and plan reviews based on 
a flawed premise, and that makes me really nervous.

Can you give me/us some background on how you came to that conclusion?

I'd really appreciate the help.
-- 

PARSLEY CONSULTING

Ken Wagoner, SET

760.745.6181 voice

760.745.0537 fax

[email protected] <mailto:[email protected]> e-mail

www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website


Brad wrote:
> I don't think this is about density at all
>
>
> -----Original Message-----
> From: A.P.Silva [mailto:[email protected]] 
> Sent: Tuesday, April 20, 2010 2:13 PM
> To: [email protected]; [email protected]
> Subject: RE: Calc Area
>
> If I understand what you are saying, it may not be correct either. If you
> use the density corresponding to 1500 SF, then you don't have to check the
> length again. If you use the density for 1640 SF, then you are right.
>
> Tony 
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Brad
> Sent: April 20, 2010 1:02 PM
> To: [email protected]; [email protected]
> Subject: RE: Calc Area
>
> Why average anything--the actual dimensions are right there-- the thing I am
> stressing is if you end up with 1640 SF area USED, go back and make sure 49'
> does not put you more than half way to ANOTHER head on the line-- the 1.2
> rule is for area USED, not minimum required area. 
>
> -----Original Message-----
> From: A.P.Silva [mailto:[email protected]]
> Sent: Tuesday, April 20, 2010 1:51 PM
> To: [email protected]; [email protected]
> Subject: RE: Calc Area
>
> The critical factor is the length of the design area. Not the number of
> heads. For 1500 RA and 1.2 shape factor this is approx. 46.5 feet. So taking
> your example, it will be 5 heads per line, whichever side is the most
> remote. Your method will work, but maybe not always. Say substitute 6' for
> 7' in your example. If the most remote area is the 8' side, now it is 6
> heads on the line. If you use your method and take 5 heads per line the
> minimum length of the design area will not be correct. 
>
> Tony  
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Bob Knight
> Sent: April 20, 2010 12:30 PM
> To: [email protected]
> Subject: RE: Calc Area
>
> George,
> The way I do this is to average the lengths between heads.  For example, you
> have a branch line with 6 heads.  They are spaced 8', 12', 9', 11', 7', &
> 10' apart.  The average will be 9.5' applying the 1.2 rule (assuming 1500
> sf) you will have 4.89 (round up to 5) heads per line. If you use the
> greatest distance of 12' you end up with only 3.87 (round up to 4) heads per
> line.  If you chose to use the least dimension of 7' you will end up with
> 6.63 (round up to 7) heads per line.  7 seems like to many and 4 looks like
> not enough.  This is why I average the distance between heads in a case such
> as yours.
>
> Bob Knight, CET
> 1660 Hill Rd
> Melba, Idaho 83641
> (208) 318-3057
> (208) 495-2057 fax
> [email protected]
> www.firebyknight.com
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of George Medina
> Jr
> Sent: Tuesday, April 20, 2010 12:41 AM
> To: [email protected]
> Subject: Calc Area
>
>
> If I am calculating a tree type system using the area/design method, and
> have several different lengths between sprinklers on a branch line. Would I
> use the longest length to determine the amount of sprinklers on a branch
> line. I have always used an average (which I've probably been wrong all
> these years).
>
> 1.2vdesign area
>            S
> S= Distance between sprinklers on branch line
>  
>
>
> 1.2vdesign area
>            S
> S= Distance between sprinklers on branch line
>  
>
>
>
> George Medina Jr. 
>
>
> No virus found in this outgoing message.
> Checked by AVG - www.avg.com 
> Version: 9.0.801 / Virus Database: 271.1.1/2820 - Release Date: 04/19/10
> 00:31:00
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
>   
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to