THAT is opening a can of worms.  What NFPA 13 and 25 require is not Backflow 
testing in the same sense as is required by Oregon (or other jurisdictions).  
We are not testing the device for its ability to prevent backflow.  We are 
flowing water through it to ensure it allows the design flow rate through the 
device. The backflow assembly doesn't even need to be touched, let alone opened 
or otherwise manipulated to conduct this test - no more than if you were 
conducting an inspector's test or main drain flow. Now you need to convince 
your plumbing AHJ of this fact...  (If my experience with some of the 
jurisdictions in Oregon is consistent, they will now require backflow testing 
licenses for folks who conduct Main Drain and ITC tests)

Mark A. Sornsin, PE | Fire Protection Engineer
Ulteig Engineers, Inc. |Fargo, ND
Direct:    701. 280.8591 | www.ulteig.com


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Doug Hicks
Sent: Tuesday, May 11, 2010 12:49 PM
To: [email protected]
Subject: Re: DCVA test connection

And in the State of Oregon, back flow testing is a licensed profession, with
another separate license for repairs.