Tom, (Emphasis in CAPS)

You didn't mention the adopted codes and standards, however if it's the
model IBC it's a mixed use BUILDING not a one/two family DWELLING. The
horizontal fire separation assembly between the mercantile and residential
USES and the vertical fire separation assembly between the dwelling UNITS
doesn't change that, it's still a mixed used BUILDING. As such the correct
fire sprinkler standard is NFPA-13. 

John Drucker, CET
Fire Protection Subcode Official 
Fire/Building/Electrical Inspector
Fire Marshals Office
Borough of Red Bank, NJ




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Tom Duross
Sent: Saturday, May 15, 2010 2:40 PM
To: [email protected]
Subject: RE: Residential Building

Well I'm back.  They didn't built it the way they drew it (so what else is
new?).
The permit said residential 2 family with retail.  Never seen this before.
Todd, I might have to poke your brain some on this, off forum.
2 1000SF condos upstairs with separate interior and exterior stairs down.
5' covered farmers porch on three sides, exterior stairs empty in at each
end.  They did say 2 hours vertically between units and 3 hours on the
retail ceiling (they state 2 hours with a head equals three on the field set
of plans).  Ton's of combustible spaces in the condos with three roof lines
and cathedral ceilings.  Wind bracing like I've never seen before.  This is
going to be a challenge because they want everything concealed (all
engineered lumber), the lofts over the bedrooms, baths and closets are open
to the living/kitchen spaces, tons of dormers with ceilings, etc.  I still
don't know why it even has to be sprinklered but it's marked on the field
set so something must have been traded is all I can tell.  Time to study.
td


I doubt if you can claim that the upstairs is 13D. Unless you have 
the appropriate fire separation, the whole building would need to be 
treated as 13. I would look at it as 13 Residential.

The test that I and a few others use id that if the areas outside the 
dwelling units are for use only by the tenants or are incidental to 
the residential occupancy, then you can use 13R/13D. Otherwise, it is 
mixed use and needs to be protected per 13.  It sounds like you have 
the latter.

Remember, the permit and the hazard are mutually exclusive.

Enjoy the Cape

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to