Is there a compelling reason why you want to use CPVC instead of 
steel going through the OH2 area? Other than gluing is easier than 
screwing? Is the space above the 3 hr ceiling combustible?


At 05:48 PM 5/30/2010, you wrote:
>Another question for anyone like me working this weekend.
>I have a riser from the residential second floor passing through the OH2
>retail first floor.
>It has a slight offset before passing down into the basement.
>I'm using CPVC for the residential second floor and would normally
>transition to steel but I'm wondering if I could use CPVC for the riser
>through the first floor and then transition to steel before passing into the
>basement.  I don't think I can but it's above a 3 hr. clg. for a 10" offset
>and then in a chase with the plumbers plastic water and sewer pipe.
>I need a life.
>TD
>
>Tyco TY-FRBs are listed for OH and I'm sure the others have
>comparable products. Given it is retail, my guess is that there could
>be products outside under the porch  during good weather (like
>today). I would continue OH on the porch as well.
>
>
>At 08:56 AM 5/26/2010, you wrote:
> >Campers:
> >
> >Following up my query from 2 weeks ago..
> >
> >I'm just looking for clarification and information on a couple of things.
> >
> >I have to sprinkler a mixed use buildings first floor retail shops with
> >sidewalls from a soffited main.
> >
> >Retail spaces are only 19' deep and I'll have sidewalls front and back.
> >
> >What are you guys using for OH listed sidewalls?
> >
> >
> >
> >The same front main will also have to serve dry sidewall heads protecting a
> >farmers porch that exterior stairs lead down into.
> >
> >The porch also extends over both retail spaces (70'), 6' wide on all three
> >sides.  Front retail entries (2) and stairs at each end.
> >
> >The ceiling of the porch has just over 6" clear against the building but
>the
> >builder is filling the entire combustible space.
> >
> >Do I have to use OH design for the porch heads?
> >
> >
> >
> >Thanks,
> >
> >TD
> >
> >Go Red Sox!
> >
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to