Therein lies my question.  Military standards defer to NFPA for calculations.  
The '05 version of 11 says C=100.  The '10 version says see NFPA 13 with the 
caveat of "other C values for corrosion-resistant piping materials.  Does this 
actually include schedule 40?  If so, then Table 22.4.4.7 merely says C=120 for 
deluge pipe.

Ryan Hinson
Burns & McDonnell
Direct: 952-656-6003 Ext 3662


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Wednesday, June 09, 2010 10:51 AM
To: [email protected]
Subject: RE: C factor change for Foam solution piping

If they are the AHJ and their standard trumps NFPA then it sounds like you're 
forced to use black steel @ C=120.
  

Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Hinson, Ryan
Sent: Wednesday, June 09, 2010 11:41 AM
To: '[email protected]'
Subject: RE: C factor change for Foam solution piping

They are Hi-Expansion Foam deluge systems.  I am referring to the distribution 
piping and this is a military project so no galvanized piping downstream of the 
proportioner is allowed per ETL 02-15 or ANG ETL 01-1-1.

Ryan Hinson
Burns & McDonnell
Direct: 952-656-6003 Ext 3662

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Wednesday, June 09, 2010 10:36 AM
To: [email protected]; [email protected]
Subject: RE: C factor change for Foam solution piping

Careful now, the SS pipe referenced there is the pipe carrying the concentrate 
from the bladder tank to the proportioner, this wording is not referring to the 
distribution piping (mains and branches). 

NFPA 11, 2010 is limiting you to galvanized pipe @ C=120,  The NFPA 13 
reference is for other corrosion resistant piping that is referred to in NFPA 
13 which could basically be only S.S. since you'd never see a plastic or copper 
foam system installed.   There are some environmental conditions that would 
require the pipe to be SS.

The viscosity of the water with a 3% solution of foam is not significantly 
different than straight water. That is why there is no real difference in 
C-values for foam-water systems versus water alone.  

NFPA 13, 12.11 is referring to the installation of High Expansion Foam systems 
which have different requirements than automatic sprinklers, hence the 
reference.   Is HEF what you're designing?  This also states HEF systems that 
ARE INSTALLED IN ADDITION TO AUTOMATIC SPRINKLERS....  so yeah kind of 
circular, each group trying to cross reference each other to make sure the 
bases are covered.  No harm done.

What kind of foam system is actually being designed?






Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Brad
Sent: Wednesday, June 09, 2010 10:30 AM
To: [email protected]
Subject: RE: C factor change for Foam solution piping

Maybe it has something to do with ...kept flooded at all times..., similar
to dry C=100, except dry galv C=120, anyway, you are probably aware of this,
but I wanted to copy (from Chemtron I think) and paste it here:

PIPING MATERIALS
Stainless steel 304, 316, brass, galvanized and
black steel pipe are suitable for use with foam
solutions. The black steel pipe is only
recommended for use with foam concentrates when
the pipe is kept flooded at all times. Stainless steel
pipe is suitable for use with foam concentrates at all
times. Galvanized pipe cannot be used with foam
concentrate.

-----Original Message-----
From: Hinson, Ryan [mailto:[email protected]] 
Sent: Tuesday, June 08, 2010 1:45 PM
To: '[email protected]'
Subject: C factor change for Foam solution piping

NFPA 11 (2005) section 4.7.2.5 says black steel piping in foam solution
piping is to be 100.  No delineation is made as to the type of system.
Hence, I've been specifying worst case of 100.

NFPA 11(2010) section 4.7.2.5 states only the requirements for galvanized
foam solution piping and refers back to NFPA 13 for other C-values.  NFPA 13
(2010) table 22 4.4.7 indicates C of 120 allowable for deluge systems such
as those feeding foam systems.  Also, NFPA 13 (2010) section 12.11.1 states
to install in accordance with NFPA 11.  Seems a bit circular.

Anyone know the reason for the change?  Am I interpreting it correctly?

Thanks,

Ryan L. Hinson, EIT, NICET III
Fire Protection Engineer, Aviation & Facilities Group
Burns & McDonnell
Minneapolis-St. Paul Office
8201 Norman Center Drive, Suite 300
Bloomington, MN 55437
Direct: 952-656-6003 Ext 3662
Fax: 952-229-2923
[email protected]
www.burnsmcd.com<BLOCKED::www.burnsmcd.com>


Proud recipient of PSMJ's Premier Award for Client Satisfaction

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to