Schedule 40 per ANG ETL 01-1-1 paras 15.6.12.1 and 15.6.12.13.

Ryan Hinson
Burns & McDonnell
Direct: 952-656-6003 Ext 3662


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Brad
Sent: Wednesday, June 09, 2010 10:49 AM
To: [email protected]
Subject: RE: C factor change for Foam solution piping

I think the ...kept flooded at all times... IS talking about the solution
piping--- with deluge this would not be the case- so now what do you use if
the gov does not want galv down stream?

-----Original Message-----
From: Hinson, Ryan [mailto:[email protected]] 
Sent: Wednesday, June 09, 2010 10:41 AM
To: '[email protected]'
Subject: RE: C factor change for Foam solution piping

They are Hi-Expansion Foam deluge systems.  I am referring to the
distribution piping and this is a military project so no galvanized piping
downstream of the proportioner is allowed per ETL 02-15 or ANG ETL 01-1-1.

Ryan Hinson
Burns & McDonnell
Direct: 952-656-6003 Ext 3662

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Wednesday, June 09, 2010 10:36 AM
To: [email protected]; [email protected]
Subject: RE: C factor change for Foam solution piping

Careful now, the SS pipe referenced there is the pipe carrying the
concentrate from the bladder tank to the proportioner, this wording is not
referring to the distribution piping (mains and branches). 

NFPA 11, 2010 is limiting you to galvanized pipe @ C=120,  The NFPA 13
reference is for other corrosion resistant piping that is referred to in
NFPA 13 which could basically be only S.S. since you'd never see a plastic
or copper foam system installed.   There are some environmental conditions
that would require the pipe to be SS.

The viscosity of the water with a 3% solution of foam is not significantly
different than straight water. That is why there is no real difference in
C-values for foam-water systems versus water alone.  

NFPA 13, 12.11 is referring to the installation of High Expansion Foam
systems which have different requirements than automatic sprinklers, hence
the reference.   Is HEF what you're designing?  This also states HEF systems
that ARE INSTALLED IN ADDITION TO AUTOMATIC SPRINKLERS....  so yeah kind of
circular, each group trying to cross reference each other to make sure the
bases are covered.  No harm done.

What kind of foam system is actually being designed?






Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brad
Sent: Wednesday, June 09, 2010 10:30 AM
To: [email protected]
Subject: RE: C factor change for Foam solution piping

Maybe it has something to do with ...kept flooded at all times..., similar
to dry C=100, except dry galv C=120, anyway, you are probably aware of this,
but I wanted to copy (from Chemtron I think) and paste it here:

PIPING MATERIALS
Stainless steel 304, 316, brass, galvanized and
black steel pipe are suitable for use with foam
solutions. The black steel pipe is only
recommended for use with foam concentrates when
the pipe is kept flooded at all times. Stainless steel
pipe is suitable for use with foam concentrates at all
times. Galvanized pipe cannot be used with foam
concentrate.

-----Original Message-----
From: Hinson, Ryan [mailto:[email protected]] 
Sent: Tuesday, June 08, 2010 1:45 PM
To: '[email protected]'
Subject: C factor change for Foam solution piping

NFPA 11 (2005) section 4.7.2.5 says black steel piping in foam solution
piping is to be 100.  No delineation is made as to the type of system.
Hence, I've been specifying worst case of 100.

NFPA 11(2010) section 4.7.2.5 states only the requirements for galvanized
foam solution piping and refers back to NFPA 13 for other C-values.  NFPA 13
(2010) table 22 4.4.7 indicates C of 120 allowable for deluge systems such
as those feeding foam systems.  Also, NFPA 13 (2010) section 12.11.1 states
to install in accordance with NFPA 11.  Seems a bit circular.

Anyone know the reason for the change?  Am I interpreting it correctly?

Thanks,

Ryan L. Hinson, EIT, NICET III
Fire Protection Engineer, Aviation & Facilities Group
Burns & McDonnell
Minneapolis-St. Paul Office
8201 Norman Center Drive, Suite 300
Bloomington, MN 55437
Direct: 952-656-6003 Ext 3662
Fax: 952-229-2923
[email protected]
www.burnsmcd.com<BLOCKED::www.burnsmcd.com>


Proud recipient of PSMJ's Premier Award for Client Satisfaction

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to