Another question: when replacing heads engaged into adjustible drop nipples mfr 
by Viking, in 1970 era, half inch pipe for drop nipple, sprinkler is k 5.6  
Is it acceptable to replace sprinkler into the drop nipple? Viking does not 
list any heads for use with these drop nipples presently. 

Forest Wilson 
Cherokee Fire 

Sent from my Verizon Wireless Phone

----- Reply message -----
From: "Brad" <[email protected]>
Date: Mon, Jun 14, 2010 4:52 pm
Subject: 3/4" pipe
To: <[email protected]>

1/2" & 3/4" steel is allowed if per 8.15.19.4.2, but not in seismic. 

-----Original Message-----
From: James Zimmerman [mailto:[email protected]] 
Sent: Monday, June 14, 2010 3:42 PM
To: [email protected]
Subject: Re: 3/4" pipe

Thanks, that is what I was over looking. Saw the pipe schedule stuff but
missed 22.4.1.2

On Mon, Jun 14, 2010 at 3:34 PM, John Drucker
<[email protected]>wrote:

> 2007 NFPA-13
>
> 22.4.1.2 Hydraulically Calculated - Pipe sizes shall be no less than 1 in.
> (25 mm) nominal for ferrous piping and 3/4 in. (20 mm) nominal for copper
> tubing or nonmetallic piping listed for fire sprinkler service.
>
> Table 22.5.2.2.1 Light Hazard Pipe Schedules - 1" Min
>
> Table 22.5.3.4 Ordinary Hazard Pipe Schedule = 1" Min
>
> Table 9.2.2.1(a) Maximum Distance Between Hangers (ft-in.)- 3/4 - Steel -
> Not Allowed (N/A)
>
> Hope that helps
>
> John Drucker, CET
> Fire Protection Subcode Official
> Fire/Building/Electrical Inspector
> Fire Marshals Office
> Borough of Red Bank, NJ
>
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of James Zimmerman
> Sent: Monday, June 14, 2010 4:07 PM
> To: [email protected]
> Subject: 3/4" pipe
>
> I have a specification that states nothing less than 1" pipe shall be used
> for a sprinkler system. Is there anywhere in NFPA 13 that prohibits the
use
> of 3/4" pipe? I know in the 2007 Edition 8.15.19 states new installations
> shall have a minimum of 1" outlets for piping supplying sprinklers below
> ceilings. This section doesn't specifically come out and state that all
> piping must be 1". In 8.15.19.4 all piping with the exception of a 4"
> nipple
> shall be 1" minimum.
> Am I missing something or is 3/4" allowed per NFPA 13?
>
> Thanks,
>
> Jim
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
to:[email protected]<to%3asprinklerforum-requ...@fire
sprinkler.org>
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
to:[email protected]<to%3asprinklerforum-requ...@fire
sprinkler.org>
> (Put the word unsubscribe in the subject field)
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to