I was wondering why they are required now, but were not in the past.

-----Original Message-----
From: Steve Leyton [mailto:[email protected]] 
Sent: Monday, July 12, 2010 10:14 AM
To: [email protected]; [email protected]
Subject: RE: Check valves on floor control stations

You can't have a single standpipe connection without a check valve.

Steve Leyton
Protection Design & Consulting
San Diego, CA




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brad
Sent: Monday, July 12, 2010 7:56 AM
To: [email protected]
Subject: RE: Check valves on floor control stations

Sorry if this has been mentioned--- on a single stand pipe connection,
without the check valve, would it be possible to do an inspector's test
on
say, the 3rd floor, without moving the flow switch on the 2nd or 4th.
Would
a flow switch 'moving backwards' send a signal? 

-----Original Message-----
From: Ron Greenman [mailto:[email protected]] 
Sent: Monday, July 12, 2010 9:26 AM
To: [email protected]
Subject: Re: Check valves on floor control stations

Think about what a check valve is for--to confine the flow of water to
one direction only (trapping a section in the example given by Damien
is a secondary positive aspect but not the reason--many cows are brown
but not all). If you have a combined pipe on a low rise structure you
typically are using a single standpipe/riser combination. All flow is
in one direction and if your pipe fails you're screwed. If a high-rise
you'll have at least two combination pipes and if one fails you'll
still have water from at least one direction. So where you used to
have flow from two directions into a loop you now have flow from one
direction into the loop with essentially an open end. If you can't
check the flow to the open end you'll just have water flowing through
the floors and it would be similar to pumping into an FDC on a
sprinkler system that didn't have a check on the incoming feed line.
You'd just pump around in a circle.

On Mon, Jul 12, 2010 at 6:26 AM, A.P.Silva <[email protected]> wrote:
> Sorry, I meant '02 editions. That was my question. Whether check
valves
were
> required in '02?
>
> As for the difference in the figures, A8.17.4.2(b) is when you don't
have
a
> fire hose connection. So no contradiction.
>
> Tony
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Todd
Williams
> Sent: July 12, 2010 3:54 AM
> To: [email protected]
> Subject: Re: Check valves on floor control stations
>
> Not sure about the '03, but it was not the case in '02. An interesting
side
> note: in both the '07 and the '10 editions, figure
> A8.17.4.2(b) shows a floor control without a check valve, but figures
> A8.17.5.2.2(a) and (b) show the floor control with a check valve.
> Since the text supports the latter, that one wins.
>
>
> At 12:11 AM 7/12/2010, you wrote:
>>I think this requirement was from the '07 editions of 13 & 14, and was
>>not a requirement in the '03 editions. Can someone please confirm.
>>
>>Tony
>>
>>_______________________________________________
>>Sprinklerforum mailing list
>>[email protected]
>>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>>For Technical Assistance, send an email to: [email protected]
>>
>>To Unsubscribe, send an email
>>to:[email protected]
>>(Put the word unsubscribe in the subject field)
>
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> 860.535.2080
> www.fpdc.com
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
AFT WA 4184/AFL-CIO, SFPE, ASCET, NFPA, AFSA, NFSA AFAA, NIBS, WSAFM,
WFC
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 5272 (20100712) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 5272 (20100712) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to