Which is what I guess is the only thing I see out here in high rises:
multiple risers, sprinkler mains looped between them on each floor,
and dead-ended branch lines. I saw a brown cow and induced all cows
were brown. My bad.

On Mon, Jul 12, 2010 at 11:45 AM, Sprinkler Academy - C Bilbo
<[email protected]> wrote:
>
> Oh, and the previous check valve requirement was for the vertical grids that 
> wre created between standpipes in a bunch of buildings out there.
>
> Heck, two supplies MUST be better than one!!!  (Until you forget to close one 
> of the valves.... thus also the sign....)
>
>
>
>
>
> It should be recognized that the above is my opinion as a member of the NFPA 
> 13 Committee on Installation Criteria representing the NFSA, and has not been 
> processed as a formal interpretation in accordance with the NFPA Regulations 
> Governing Committee Projects and should therefore not be considered, nor 
> relied upon, as the official position of the NFPA, nor any of their technical 
> committees.
>
> Sincerely,
>
>
> Cecil Bilbo
> Academy of Fire Sprinkler Technology
> Champaign, IL
> 217-363-2460
> www.sprinkleracademy.com
>
>
>
>
>
>
> ----------------------------------------
>> From: [email protected]
>> To: [email protected]
>> Subject: RE: Check valves on floor control stations
>> Date: Mon, 12 Jul 2010 18:42:27 +0000
>>
>>
>> Brad and Damien,
>>
>> The new requirement for the check valve tracks with the NFPA 14 committee's 
>> desire to see one there. they had good reasons, because any water left in a 
>> system is a good thing for a couple of reasons. One, it will allow SOEMTHING 
>> to come out if there is a fire while the system is closed. Second, you 
>> wouldn't have to fill every floor of the building if you drained the entire 
>> building (and you wouldn't have to close each floor's control valve. That is 
>> a good thing. And if you don't have to clase a valve on each floor, then you 
>> won't forget to open one either.
>>
>> The 13 Committee was offended that the NFPA 14 Committee was trying to place 
>> a check on the Sprinkler System. (Tongue in Cheek....) But they eventually 
>> relented and agreed.
>>
>>
>>
>>
>>
>> It should be recognized that the above is my opinion as a member of the NFPA 
>> 13 Committee on Installation Criteria representing the NFSA, and has not 
>> been processed as a formal interpretation in accordance with the NFPA 
>> Regulations Governing Committee Projects and should therefore not be 
>> considered, nor relied upon, as the official position of the NFPA, nor any 
>> of their technical committees.
>>
>> Sincerely,
>>
>>
>> Cecil Bilbo
>> Academy of Fire Sprinkler Technology
>> Champaign, IL
>> 217-363-2460
>> www.sprinkleracademy.com
>>
>>
>>
>>
>>
>>
>> ----------------------------------------
>>> From: [email protected]
>>> To: [email protected]
>>> Subject: RE: Check valves on floor control stations
>>> Date: Mon, 12 Jul 2010 10:48:03 -0500
>>>
>>> Thanks mike. So before checks were required for single connections,
>>> individual floors could be tested with-out taking the rest of the floors out
>>> of service. It seems the only reason they are required now is the 'drain
>>> thing'.
>>>
>>> -----Original Message-----
>>> From: Mike Henke [mailto:[email protected]]
>>> Sent: Monday, July 12, 2010 10:39 AM
>>> To: [email protected]
>>> Subject: RE: Check valves on floor control stations
>>>
>>> Flowswitches will not operate if the water flows backward and they will
>>> not be damaged either.
>>>
>>> Regards,
>>>
>>> mike
>>>
>>> Mike Henke CET
>>> Sprinkler Product Manager
>>> 1-800-325-3936
>>> 314-595-6740 Direct
>>> www.pottersignal.com
>>>
>>>
>>> -----Original Message-----
>>> From: [email protected]
>>> [mailto:[email protected]] On Behalf Of Steve
>>> Leyton
>>> Sent: Monday, July 12, 2010 10:14 AM
>>> To: [email protected]; [email protected]
>>> Subject: RE: Check valves on floor control stations
>>>
>>> You can't have a single standpipe connection without a check valve.
>>>
>>> Steve Leyton
>>> Protection Design & Consulting
>>> San Diego, CA
>>>
>>>
>>>
>>>
>>> -----Original Message-----
>>> From: [email protected]
>>> [mailto:[email protected]] On Behalf Of Brad
>>> Sent: Monday, July 12, 2010 7:56 AM
>>> To: [email protected]
>>> Subject: RE: Check valves on floor control stations
>>>
>>> Sorry if this has been mentioned--- on a single stand pipe connection,
>>> without the check valve, would it be possible to do an inspector's test
>>> on
>>> say, the 3rd floor, without moving the flow switch on the 2nd or 4th.
>>> Would
>>> a flow switch 'moving backwards' send a signal?
>>>
>>> -----Original Message-----
>>> From: Ron Greenman [mailto:[email protected]]
>>> Sent: Monday, July 12, 2010 9:26 AM
>>> To: [email protected]
>>> Subject: Re: Check valves on floor control stations
>>>
>>> Think about what a check valve is for--to confine the flow of water to
>>> one direction only (trapping a section in the example given by Damien
>>> is a secondary positive aspect but not the reason--many cows are brown
>>> but not all). If you have a combined pipe on a low rise structure you
>>> typically are using a single standpipe/riser combination. All flow is
>>> in one direction and if your pipe fails you're screwed. If a high-rise
>>> you'll have at least two combination pipes and if one fails you'll
>>> still have water from at least one direction. So where you used to
>>> have flow from two directions into a loop you now have flow from one
>>> direction into the loop with essentially an open end. If you can't
>>> check the flow to the open end you'll just have water flowing through
>>> the floors and it would be similar to pumping into an FDC on a
>>> sprinkler system that didn't have a check on the incoming feed line.
>>> You'd just pump around in a circle.
>>>
>>> On Mon, Jul 12, 2010 at 6:26 AM, A.P.Silva wrote:
>>>> Sorry, I meant '02 editions. That was my question. Whether check
>>> valves
>>> were
>>>> required in '02?
>>>>
>>>> As for the difference in the figures, A8.17.4.2(b) is when you don't
>>> have
>>> a
>>>> fire hose connection. So no contradiction.
>>>>
>>>> Tony
>>>>
>>>> -----Original Message-----
>>>> From: [email protected]
>>>> [mailto:[email protected]] On Behalf Of Todd
>>> Williams
>>>> Sent: July 12, 2010 3:54 AM
>>>> To: [email protected]
>>>> Subject: Re: Check valves on floor control stations
>>>>
>>>> Not sure about the '03, but it was not the case in '02. An interesting
>>> side
>>>> note: in both the '07 and the '10 editions, figure
>>>> A8.17.4.2(b) shows a floor control without a check valve, but figures
>>>> A8.17.5.2.2(a) and (b) show the floor control with a check valve.
>>>> Since the text supports the latter, that one wins.
>>>>
>>>>
>>>> At 12:11 AM 7/12/2010, you wrote:
>>>>>I think this requirement was from the '07 editions of 13 & 14, and was
>>>>>not a requirement in the '03 editions. Can someone please confirm.
>>>>>
>>>>>Tony
>>>>>
>>>>>_______________________________________________
>>>>>Sprinklerforum mailing list
>>>>>[email protected]
>>>>>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>>>
>>>>>For Technical Assistance, send an email to: [email protected]
>>>>>
>>>>>To Unsubscribe, send an email
>>>>>to:[email protected]
>>>>>(Put the word unsubscribe in the subject field)
>>>>
>>>> Todd G. Williams, PE
>>>> Fire Protection Design/Consulting
>>>> Stonington, CT
>>>> 860.535.2080
>>>> www.fpdc.com
>>>>
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>>
>>>> For Technical Assistance, send an email to: [email protected]
>>>>
>>>> To Unsubscribe, send an email
>>> to:[email protected]
>>>> (Put the word unsubscribe in the subject field)
>>>>
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>>
>>>> For Technical Assistance, send an email to: [email protected]
>>>>
>>>> To Unsubscribe, send an email
>>> to:[email protected]
>>>> (Put the word unsubscribe in the subject field)
>>>>
>>>
>>>
>>>
>>> --
>>> Ron Greenman
>>> Instructor
>>> Fire Protection Engineering
>>> Bates Technical College
>>> Tacoma, WA
>>>
>>> Member:
>>> AFT WA 4184/AFL-CIO, SFPE, ASCET, NFPA, AFSA, NFSA AFAA, NIBS, WSAFM,
>>> WFC
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>
>>> For Technical Assistance, send an email to: [email protected]
>>>
>>> To Unsubscribe, send an email
>>> to:[email protected]
>>> (Put the word unsubscribe in the subject field)
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>
>>> For Technical Assistance, send an email to: [email protected]
>>>
>>> To Unsubscribe, send an email
>>> to:[email protected]
>>> (Put the word unsubscribe in the subject field)
>>>
>>>
>>> __________ Information from ESET NOD32 Antivirus, version of virus
>>> signature database 5272 (20100712) __________
>>>
>>> The message was checked by ESET NOD32 Antivirus.
>>>
>>> http://www.eset.com
>>>
>>>
>>>
>>> __________ Information from ESET NOD32 Antivirus, version of virus
>>> signature database 5272 (20100712) __________
>>>
>>> The message was checked by ESET NOD32 Antivirus.
>>>
>>> http://www.eset.com
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>
>>> For Technical Assistance, send an email to: [email protected]
>>>
>>> To Unsubscribe, send an email
>>> to:[email protected]
>>> (Put the word unsubscribe in the subject field)
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>
>>> For Technical Assistance, send an email to: [email protected]
>>>
>>> To Unsubscribe, send an email to:[email protected]
>>> (Put the word unsubscribe in the subject field)
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>
>>> For Technical Assistance, send an email to: [email protected]
>>>
>>> To Unsubscribe, send an email to:[email protected]
>>> (Put the word unsubscribe in the subject field)
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
AFT WA 4184/AFL-CIO, SFPE, ASCET, NFPA, AFSA, NFSA AFAA, NIBS, WSAFM, WFC
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to