Interesting point, but there is arguably no more nor less fire load at
the perimeter of a residential compartment where the windows occur, so
the hazard group is the same ... in theory.

 

Steve Leyton

Protection Design & Consulting

San Diego, CA

 

 

 

From: Jeff Hewitt [mailto:[email protected]] 
Sent: Thursday, July 15, 2010 12:26 PM
To: Steve Leyton; [email protected]
Subject: RE: Small Orifice Sprinklers in Water Curtain

 

Steve,

Just thinking out loud, and do not have a copy of 13 in front of me....

Aren't closely spaced sprinklers and water curtains listed outside of
the occupancy classification section?  I am not certain that a water
curtain configuration can be classified as "Light Hazard", and if it
cannot, then your argument loses validity.

Jeff Hewitt, PE, SET, SFPE (Professional Member)

Corporate Engineer

Bi-State Fire Protection Corporation

241 Hughes Lane

St. Charles, MO  63301

636-946-0011

636-946-5172 (fax)

314-574-6989 (cell)

Fire Sprinklers Save lives.

Can You Live Without Them?

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Steve
Leyton
Sent: Thursday, July 15, 2010 2:12 PM
To: [email protected]
Subject: Small Orifice Sprinklers in Water Curtain

Scenario:             3-story Light Hazard (Residential) occupancy,

fully sprinklered per 13.

Situation:             Exterior exit stairs are too close to glazed

openings in exterior walls and 45-minute window protection is required

(from inside out) for several 2'x3' fixed windows on all three floors.

Challenge:           Can't use window sprinklers because exterior walls

are bearing.   Am proposing to use water curtain provisions of the

building code, and furnish 3 GPM per lineal foot per 13.

 

Question:            Since the windows are only 2' wide, and there are

up to 3 windows in a cluster, we will have sprinklers at 4' apart in

several areas and will be provided a baffle of some sort.    I can

easily hit my minimum flow rate with small orifice sprinklers and do not

see any restriction in 13 regarding orifice size in a water curtain.

Since it's all Light Hazard, can anyone think of a reason why we can't

use 4.2K pendents?

 

Steve Leyton

PROTECTION DESIGN & CONSULTING

2851 Camino del Rio South, Suite 400

San Diego, CA 92108

-------------------------------------------------------------

Ph:      858.751.2930 - ext. 102

Fax:    858.751.2933

Cell:  619.972.5696

 

 

 

 

_______________________________________________

Sprinklerforum mailing list

[email protected]

http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]

(Put the word unsubscribe in the subject field)



__________ Information from ESET NOD32 Antivirus, version of virus
signature database 5282 (20100715) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to