Steve,

 

I do not disagree, just wanted to make the point.  Also, if the AHJ accepts
it, that would be another route to take.

 

Jeff Hewitt, PE, SET, SFPE (Professional Member)

Corporate Engineer

Bi-State Fire Protection Corporation

 

241 Hughes Lane

St. Charles, MO  63301

636-946-0011

636-946-5172 (fax)

314-574-6989 (cell)

 

Fire Sprinklers Save lives.

Can You Live Without Them?

 

From: Steve Leyton [mailto:[email protected]] 
Sent: Thursday, July 15, 2010 2:37 PM
To: Jeff Hewitt; [email protected]
Subject: RE: Small Orifice Sprinklers in Water Curtain

 

Interesting point, but there is arguably no more nor less fire load at the
perimeter of a residential compartment where the windows occur, so the
hazard group is the same . in theory.

 

Steve Leyton

Protection Design & Consulting

San Diego, CA

 

 

 

From: Jeff Hewitt [mailto:[email protected]] 
Sent: Thursday, July 15, 2010 12:26 PM
To: Steve Leyton; [email protected]
Subject: RE: Small Orifice Sprinklers in Water Curtain

 

Steve,

Just thinking out loud, and do not have a copy of 13 in front of me....

Aren't closely spaced sprinklers and water curtains listed outside of the
occupancy classification section?  I am not certain that a water curtain
configuration can be classified as "Light Hazard", and if it cannot, then
your argument loses validity.

Jeff Hewitt, PE, SET, SFPE (Professional Member)

Corporate Engineer

Bi-State Fire Protection Corporation

241 Hughes Lane

St. Charles, MO  63301

636-946-0011

636-946-5172 (fax)

314-574-6989 (cell)

Fire Sprinklers Save lives.

Can You Live Without Them?

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Steve Leyton
Sent: Thursday, July 15, 2010 2:12 PM
To: [email protected]
Subject: Small Orifice Sprinklers in Water Curtain

Scenario:             3-story Light Hazard (Residential) occupancy,

fully sprinklered per 13.

Situation:             Exterior exit stairs are too close to glazed

openings in exterior walls and 45-minute window protection is required

(from inside out) for several 2'x3' fixed windows on all three floors.

Challenge:           Can't use window sprinklers because exterior walls

are bearing.   Am proposing to use water curtain provisions of the

building code, and furnish 3 GPM per lineal foot per 13.

 

Question:            Since the windows are only 2' wide, and there are

up to 3 windows in a cluster, we will have sprinklers at 4' apart in

several areas and will be provided a baffle of some sort.    I can

easily hit my minimum flow rate with small orifice sprinklers and do not

see any restriction in 13 regarding orifice size in a water curtain.

Since it's all Light Hazard, can anyone think of a reason why we can't

use 4.2K pendents?

 

Steve Leyton

PROTECTION DESIGN & CONSULTING

2851 Camino del Rio South, Suite 400

San Diego, CA 92108

-------------------------------------------------------------

Ph:      858.751.2930 - ext. 102

Fax:    858.751.2933

Cell:  619.972.5696

 

 

 

 

_______________________________________________

Sprinklerforum mailing list

[email protected]

http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]

(Put the word unsubscribe in the subject field)



__________ Information from ESET NOD32 Antivirus, version of virus signature
database 5282 (20100715) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com



__________ Information from ESET NOD32 Antivirus, version of virus signature
database 5282 (20100715) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to