Sorry I am so late to post.  Note that the following is a should not a shall... 
 NFPA 20, 07 ed. A.5.12 ...Access to the pump room should be provided from 
outside the building...


Reed A. Roisum, CET
Ulteig Engineers, Inc.





-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Dewayne Martinez
Sent: Wednesday, July 14, 2010 1:00 PM
To: [email protected]
Subject: RE: fire pump room - external door?

Thanks guys, that is what I thought.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Tom
Duross
Sent: Wednesday, July 14, 2010 12:07 PM
To: [email protected]
Subject: RE: fire pump room - external door?

I believe that's a building code issue.  Ours calls for protected egress
if no direct access.
TD


Does a fire pump room, with a electric fire pump, that is located on a
exterior wall require a exterior door?
I know it is good practice to have one but this is an existing facility
where a fire pump is being installed.

Thanks,
Dewayne

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to