9.3.6.6 ('07 Ed.) requires sprigs over 4'-0" to be restrained, but not
braced.

Benjamin Young



On Tue, Aug 10, 2010 at 9:21 AM, Reed Roisum <[email protected]> wrote:

> 4-way bracing is required on all risers over 3 ft in length.  A riser is
> defined as a vertical supply pipe.  I assume you are wondering if a sprig
> needs to be 4-way braced if it is over 3 ft. in length?  A sprig is a
> vertical supply pipes but it is also defined separately so I would say no
> you would not need to brace and sway bracing is required only on BLs that
> are greater than 2 in dia. so I would say that would apply to the sprigs
> because a sprig is a BL by definition.
>
> Now a RN over 3 ft. in length just going by the definitions looks like it
> would need to be braced.
>
> Might want to check the archives cuz I think this was hashed out a couple
> of years ago??
>
>
> Reed A. Roisum, CET
> Ulteig Engineers, Inc.
>
>
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of Brian Harris
> Sent: Tuesday, August 10, 2010 7:39 AM
> To: [email protected]
> Subject: 4-WAY BRACES
> Importance: High
>
> Forum-
> What is the general consensus about putting 4-way braces on "any" vertical
> pipe that is over 3 feet long? I was under the impression it was for Risers
> only, is that not the case?
>
> Thanks!
>
>
> Brian Harris
>
>
>
>
>
>
> Design Engineer
>
>
>
> First Defense Fire Protection
> 11957 Ramah Church Road
> Huntersville NC 28078
>
>
>
>
> [email protected]
> www.firstdefensefire.com <outbind://80/www.firstdefensefire.com>
>
>
>
> Ph: 704.948.3506
> Fax: 704.948.3507
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to