Hello Todd,

Tyco has a heat trace listed for branch lines they are proud of. I had to use 
some and about 95' of cable, 3 sets of ends and a controller was about 
$2.500.00 plus installation.

Friday, August 20, 2010, 11:37:58 AM, you wrote:

> I don't think heat trace would be approved for 
> this use (at this point). I believe it is only for mains.

> An enclosure may be the only alternative, not 
> knowing the dimension of the units involved. It 
> would just need to be an insulated box, since we 
> are enclosing a furnace and residual heat would probably keep the space warm.

> Sounds like a good pilot project.




> At 10:46 AM 8/20/2010, you wrote:
>>You could use heat tracing. (...not a great idea, but it would work)

>>Matt Grisé PE*, LEED AP
>>Sales Engineer
>>Alliance Fire Protection
>>*Licensed in KS & MO

>>913.888.0647 ph
>>913.888.0618 f
>>913.927.0222 cell
>>www. AFPsprink.com


>>-----Original Message-----
>>From: [email protected] 
>>[mailto:[email protected]] On Behalf Of George Church
>>Sent: Friday, August 20, 2010 9:45 AM
>>To: [email protected]
>>Subject: 13D attic Fuel-fired protection

>>In those areas with cold weather and 13D in place, has anyone come up with a
>>resolution for protecting a head above the fuel fired furnace in an
>>unconditioned attic space short of walling it off so a wet pipe could be
>>safe?
>>We certainly want to minimize the impact at this critical time in our IRC
>>mandate here in PA, so that we can provide the builders and homeowners with
>>an affordable, smooth transition to a sprinklered Commonwealth.

>>Losing AF is quite a blow, even if its temporary (I hope!) for areas where
>>50-50 works. It'd take a really tall dry upright, past the listing
>>limitation.

>>From: George Church [mailto:[email protected]]
>>Sent: Friday, August 20, 2010 10:39 AM
>>To: 'Tim Knisely'
>>Subject: RE: Sprinkler question...

>>Without antifreeze, its seal it in and pop a wet head in it, or install a
>>tiny dry system. I'm confident that the additional testing will soon allow
>>premix 50-50 solutions and we'll be back to a small AF loop for a head in
>>the attic atop the unit.
>>I would argue passionately that sticking a furnace in an attic does NOT make
>>the space conditioned sufficiently for a wet pipe to survive a winter around
>>here.

>>Tyco now has a CPVC dry system and residential dry pendents, but that's a
>>huge expense for a single head. Even an AF loop with the RPZ and associated
>>backflow and fluid maintenance chores introduces too much complexity for 13D
>>IMHO.
>>We should be thinking of these as Install and Forget- because that is what
>>will happen.

>>Will check around- I'm posting this to the AFSA Sprinkler Forum to see if
>>anyone has additional thoughts.

>>George Church'
>>Rowe Sprinkler
>>[email protected]
>>570-837-7647
>>From: Tim Knisely [mailto:[email protected]]
>>Sent: Friday, August 20, 2010 8:46 AM
>>To: 'George L. Church Jr.'
>>Subject: Sprinkler question...

>>George,

>>With sprinklers now required in unfinished attics where a fuel-fired
>>appliance is located, what is the preferred method to keep this from
>>freezing?  I've heard some people say that the space is now heated and the
>>head won't freeze.  But, I'm not sure if some of the newer high-efficiency
>>furnaces put off that much heat.  One option is to frame in a room to
>>capture the heat, but curious to see what some others might be.

>>Thanks.

>>Tim E. Knisely, Senior Fire Inspector
>>Centre Region Code Administration
>>2643 Gateway Drive, Suite #2
>>State College, PA  16801
>>(814) 231-3058
>>(814) 231-3088 Fax
>>E-mail: [email protected]


>>_______________________________________________
>>Sprinklerforum mailing list
>>[email protected]
>>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

>>For Technical Assistance, send an email to: [email protected]

>>To Unsubscribe, send an email to:[email protected]
>>(Put the word unsubscribe in the subject field)
>>_______________________________________________
>>Sprinklerforum mailing list
>>[email protected]
>>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

>>For Technical Assistance, send an email to: [email protected]

>>To Unsubscribe, send an email to:[email protected]
>>(Put the word unsubscribe in the subject field)

> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> 860.535.2080
> www.fpdc.com

> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

> For Technical Assistance, send an email to: [email protected]

> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)



-- 
Best regards,
 Charles Thurston                            mailto:[email protected]
  Coastal Fire Protection/ Myrtle Beach Fire & Safety Group.
   AFAA Guest

Electronic Privacy Notice:
This e-mail, and any attachments, contains information that is, or may  
be, covered by electronic communications privacy laws, and is also  
confidential and proprietary in nature. If you are not the intended  
recipient, please be advised that you are legally prohibited from  
retaining, using, copying, distributing, or otherwise disclosing this  
information in any manner. Instead, please reply to the sender that  
you have received this communication in error, and then immediately  
delete it. Thank you in advance for your cooperation

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to