Tyco has the DS-1 dry upright to 48", that would give you about 36" useable
height above insulation. If that is not enough we've built small vertical
chases with Dry HSW adjacent to the units. These chases must be well
insulated, and open to the ambient heat from below. We've installed a false
return air grill at the bottom to ensure that the heat could get into the
chase, and let hot air rising and cold air falling do the rest.

As far as listing goes since 8.6.5.1 allows the use of QR both of these
should work as they can both be QR. Additionally the DS-1 is available up to
286'F so the summer attic temp should not be a problem.

Thom

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Matt Grise
Sent: Friday, August 20, 2010 8:46 AM
To: '[email protected]'
Subject: RE: 13D attic Fuel-fired protection

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George Church
Sent: Friday, August 20, 2010 9:45 AM
To: [email protected]
Subject: 13D attic Fuel-fired protection

In those areas with cold weather and 13D in place, has anyone come up with a
resolution for protecting a head above the fuel fired furnace in an
unconditioned attic space short of walling it off so a wet pipe could be
safe?
We certainly want to minimize the impact at this critical time in our IRC
mandate here in PA, so that we can provide the builders and homeowners with
an affordable, smooth transition to a sprinklered Commonwealth.

Losing AF is quite a blow, even if its temporary (I hope!) for areas where
50-50 works. It'd take a really tall dry upright, past the listing
limitation.

From: George Church [mailto:[email protected]] 
Sent: Friday, August 20, 2010 10:39 AM
To: 'Tim Knisely'
Subject: RE: Sprinkler question...

Without antifreeze, its seal it in and pop a wet head in it, or install a
tiny dry system. I'm confident that the additional testing will soon allow
premix 50-50 solutions and we'll be back to a small AF loop for a head in
the attic atop the unit.
I would argue passionately that sticking a furnace in an attic does NOT make
the space conditioned sufficiently for a wet pipe to survive a winter around
here.

Tyco now has a CPVC dry system and residential dry pendents, but that's a
huge expense for a single head. Even an AF loop with the RPZ and associated
backflow and fluid maintenance chores introduces too much complexity for 13D
IMHO.
We should be thinking of these as Install and Forget- because that is what
will happen.

Will check around- I'm posting this to the AFSA Sprinkler Forum to see if
anyone has additional thoughts.

George Church'
Rowe Sprinkler
[email protected]
570-837-7647
From: Tim Knisely [mailto:[email protected]] 
Sent: Friday, August 20, 2010 8:46 AM
To: 'George L. Church Jr.'
Subject: Sprinkler question...

George, 

With sprinklers now required in unfinished attics where a fuel-fired
appliance is located, what is the preferred method to keep this from
freezing?  I've heard some people say that the space is now heated and the
head won't freeze.  But, I'm not sure if some of the newer high-efficiency
furnaces put off that much heat.  One option is to frame in a room to
capture the heat, but curious to see what some others might be.

Thanks.  

Tim E. Knisely, Senior Fire Inspector
Centre Region Code Administration
2643 Gateway Drive, Suite #2
State College, PA  16801
(814) 231-3058
(814) 231-3088 Fax
E-mail: [email protected]


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to