If your IFC, the following from appendix B, may apply to your project.

B105.2 Buildings other than one- and two-family dwellings.
The minimum fire-flow and flow duration for buildings other
than one- and two-family dwellings shall be as specified in
Table B105.1.
Exception: A reduction in required fire-flow of up to 75
percent, as approved, is allowed when the building is provided
with an approved automatic sprinkler system installed
in accordance with Section 903.3.1.1 or 903.3.1.2. The
resulting fire-flow shall not be less than 1,500 gallons per
minute (5678 L/min) for the prescribed duration as specified
in Table B105.1.