Not sure what your point is Thom. The fire flow table is in the appendix of the Code, and at the top of the page it clearly states the appendix is not mandatory, so IFC Appendix B is not automatically adopted when the IFC is. Different jurisdictions apply different methods for this issue.
IFC 508.3 States that "Fire flow requirements.... shall be determined by an approved method." So who would approve that method? ..........drum roll............... The AHJ. The AHJ directs you to what method has been approved in his jurisdiction then you use that method to do the calcs. It just so happens with this issue that there is no set standard. See 508.3 above. You don't go by a number someone pulls out of a hat. You use the recognized method to make the determination. The other reason for getting the direction from the AHJ is that the fire flow values can vary greatly depending on what method is used for making the calculations. And I kept stating IBC when it should have been IFC, sorry for any confusion there. Craig L. Prahl, CET Fire Protection Specialist Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive Spartanburg, SCĀ 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [email protected] http://www.ch2m.com -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Thom Sent: Wednesday, September 08, 2010 5:46 PM To: [email protected] Subject: RE: Dual Purpose Fire Pump - Hydrants and Sprinklers So why would we rely on a written and adopted code or standard! Oh that's right, because when we end up in court we have a written adopted document to support or position. That usually works out better than, "Well I polled the AHJ, the insurance underwriter, the Arch, the building Dept. and the guy from the dog pound, and they all thought 1000GPM would be Ok." You can do anything you want if you're ready to accept the accompanying liability. If not--- -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of [email protected] Sent: Wednesday, September 08, 2010 3:19 PM To: [email protected] Subject: RE: Dual Purpose Fire Pump - Hydrants and Sprinklers Don't make that assumption. Fire flow is one thing that has no universal rules and has no regard for the applicable building code. _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)