The standard gasket is EPDM which does not play well with oil. If you have a 
lot of evidence of oil in the system use Buna gasket. Check any of the gasket 
selection guides. 
Sent on the Sprint® Now Network from my BlackBerry®

-----Original Message-----
From: Ryan Peterson <[email protected]>
Sender: [email protected]
Date: Tue, 28 Sep 2010 11:23:37 
To: [email protected]<[email protected]>
Reply-To: [email protected]
Subject: Oil Filled Air Compressors in Dry Systems

I'm interested in the groups experiences and comments about using oil filled 
compressors in dry systems. The reason I broach the subject is that many 
coupling manufacturers include in their datasheet: "Approved by Factory Mutual 
Research for wet and dry (oil free air) sprinkler services up to the rated 
working pressure".  Without an air/oil separator installed in the air supply 
line some of the air compressor oil is going to make it in the system.  Oil 
filled compressors are cheaper (in some cases) than oil less; and cheaper is 
good practice these days as long as the rules are followed. 

Thanks,

Ryan Peterson
Design Manager
Wayne Automatic Fire Sprinklers

Office 407-877-5593
Cell 904-838-7020
Fax 407-656-8036


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to