13, 2007; 11.2.3.2.2.3 requires area density curve or 5 heads whichever is
most demanding. When a room design method is used for a room such as a motel
room with one E/C head and two standard heads all you would need to
calculate is the 3 heads in the room, assuming the openings are protected.
This is what I think, but someone was asking whether 5 E/C heads should be
calculated. My opinion is 11.2.3.2.2.3 does not apply for room design method
and 5 E/C heads need not be calculated. But thought I will throw it at the
forum before giving him a reply.

Tony 