I have a R2 occupancy that is to be sprinklered per NFPA13R (07ed). The architect wants to use quick response institutional sprinklers. It appears that per 6.7.7.1.3 I can use QR sprinklers inside the dwelling unit only if it meets the definition of a compartment with no more than 4 sprinklers. If the dwelling unit contains multiple rooms (ie: bathroom, kitchen, ect.) then this unit would not qualify because it is not single compartment correct? What if with all the compartments together there would only be 4 sprinklers? Thanks, Dewayne Martinez Design Build Fire Protection New Berlin, WI <http://www.designbuildfire.com/> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum