Cliff,

Chris is on the right track. There is nothing I know of that provides "blast protection" for sprinkler systems. The impact loading of a blast is probably a lot more severe than an earthquake and what we normally use might not do much of anything. The EOR needs to provide you with specifics. I would start with an RFI stating that there is currently no bracing listed for blast protection and to advise on materials and methods.



At 05:58 PM 11/10/2010, you wrote:
 I have an unusual situation on a project and would like some opinions.

We are currently doing a project where seismic bracing has been specified
for 'blast protection' (or something like that).  The project is not in a
zone that would otherwise require seismic protection.  So here is my
question.

Are restraining straps required to be installed on the beam clamps?

Now before you answer, consider this - NFPA 13 2007 - 9.3.7.1 - C-type
clamps ... used to attach hangers to the building structure IN AREAS SUBJECT
TO EARTHQUAKES shall be equipped with a retraining strap.

Ok, now what is your opinion?

Thanks,

Cliff Whitfield, SET
President
Fire Design, Inc.
850-526-1886

[email protected]
www.fire-design.com


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to