You're missing the code citation he can't furnish. If it works
hydraulically, it works.
I recall a raised eyebrow on a 4" riser feeding a 6" crossmain; very simply,
I used the excess pressure where it saved my boss the most money, in the
riser devices. But nothing in 13 says you need to go from big to small
consistently.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Thursday, November 11, 2010 8:51 AM
To: [email protected]
Subject: reduce then increase pipe sizes

I am working on an existing system where we have to tie in a new 2-1/2" main
into an existing 3". Since they do not make a 3x2-1/2 mechanical tee, that
option is out. My proposal is to utilize an existing plugged 2" outlet,
install a 2 x 0-6 TxG nipple and then increase to 2-1/2". It works
hydraulically with 18+ psi left over (reducing the 2-1/2" main not an option
hydraulically).

I don't see anything in the Code that states that it is not allowed. 
However, the AHJ says it isn't. Before I argue the point, am I missing
something?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to