With your subrogation work do you really believe supervised low air protects
against false trips.  Sometimes yes sometimes no IMHO.  How about the one
where the alarm rang for days before the freezer tripped and we got to take
the sprinkler system to the parking lot for a couple days.  Or sometimes the
air compressor runs nearly constantly from a larger leak masking the leak
and finally fails only then revealing the leak before anyone has a real
chance to react to the low air alarm before it trips.  

But I think we digressed.  I wouldn't allow the head if involved.  Just not
worth the risk IMHO.  I though agree it would probably work.  Good news is
they only have to last 10 years.

Chris