I guess it's too late to take the dry off city only, before the pump--
(usually in this set-up, the parking goes down and the high rise goes up)--
If 20 ft/sec was spec'd, city water only might not have been utilized-- I
can see 50 pound safety on HUGE dry systems, AND the xtra heavy DP dilemma.

-----Original Message-----
From: David de Vries [mailto:[email protected]] 
Sent: Friday, November 12, 2010 5:56 PM
To: [email protected]
Subject: RE: High Pressure Dry Pendents

Sure, I have seen a fair number of popped circuit breakers, switches shut
off, etc. and the air compressor is off, but this is a high rise building
with all the bells and whistles.  Fire alarm panel will be monitored by the
complex and by the municipal remote station.  If there is a low air alarm
(yes, I have seen those fail also), people will know.  
 
That said, I am still not comfortable allowing the 175 sprinklers in a
system that will see about 215 when it trips.  Considering all options,
including running exposed piping with high pressure uprights in the
finished ceiling area (architect throws fit here), install a PRV ahead of
the DPV (contractor throws fit here), separating and heating the finished
ceiling areas and use high pressure pendents on return bends (everyone who
has to come up with money throws fit here), etc.

Dave 

David A. de Vries, P.E., CSP 
Firetech Engineering Incorporated 



--- On Fri, 11/12/10, Chris Cahill <[email protected]> wrote:


From: Chris Cahill <[email protected]>
Subject: RE: High Pressure Dry Pendents
To: [email protected]
Date: Friday, November 12, 2010, 7:50 AM


With your subrogation work do you really believe supervised low air protects
against false trips.  Sometimes yes sometimes no IMHO.  How about the one
where the alarm rang for days before the freezer tripped and we got to take
the sprinkler system to the parking lot for a couple days.  Or sometimes the
air compressor runs nearly constantly from a larger leak masking the leak
and finally fails only then revealing the leak before anyone has a real
chance to react to the low air alarm before it trips.  

But I think we digressed.  I wouldn't allow the head if involved.  Just not
worth the risk IMHO.  I though agree it would probably work.  Good news is
they only have to last 10 years.

Chris

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of David de
Vries
Sent: Thursday, November 11, 2010 6:21 PM
To: [email protected]
Subject: RE: High Pressure Dry Pendents

 
Chris, we are designing to avoid the false trip from a dead compressor
(supervised low air), but maybe a little hammer from the fire pump starting
from a dead jockey pump will trip the DPV.  Then you are right; we get the
full static pressure.
 
 

Dave 

David A. de Vries, P.E., CSP 
Firetech Engineering Incorporated 
2715 Harrison St. 
Evanston, IL 60201 
Tel: 847-733-0944 
Fax: 847-866-6255 



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to