Brian,

My approach would be as follows:

1) Refer the AHJ to section 4.6.2.3.1 of NFPA-20, 2010, which states [emphasis mine]: /4.6.2.3.1 Where the maximum flow available from the water supply cannot provide a flow of 150 percent of the rated flow of the pump, but the water supply can provide the greater of 100 percent of rated flow or the maximum flow demand of the fire protection system(s), the water supply _*shall be deemed to be adequate*_. In this case, the maximum flow shall be considered the highest flow that the water supply can achieve
/
2) Follow the requirement in 4.6.2.3.2 which requires that a sign be added to the pump room, to advise any future testing personnel that the available water supply does not allow for testing to 150 percent of rated capacity: /4.6.2.3.2 Where the water supply cannot provide 150 percent of the rated flow of the pump, a placard shall be placed in the pump room indicating the minimum suction pressure that the fire pump is allowed to be tested at and also indicating the required flow rate./

3) Similar language is provided in section 4.6.5.1, and 4.6.5.2 of NFPA-20, 2010 [emphasis mine]: /4.6.5.1 Except as provided in 4.6.5.2, the head available from a water supply shall be figured on the basis of a flow of 150 percent of rated capacity of the fire pump.

4.6.5.2 Where the water supply cannot provide a flow of 150 percent of the rated flow of the pump, but the water supply can provide the flow demand of the fire protection system, the head available from the water supply _*shall be permitted*_ to be calculated on the basis of the maximum flow available as allowed by 4.6.2.3.1.
/
Seems to me from reading this, that his concerns of the pump running up to 150% of capacity drawing his municipal main down to 18.7 psi has been addressed by the NFPA-20 committee.

sincerely,
--

PARSLEY CONSULTING

Ken Wagoner, SET

760.745.6181 voice

760.745.0537 fax

[email protected] <mailto:[email protected]>e-mail

www.ParsleyConsulting.com <http://www.ParsleyConsulting.com>website


IMPORTANT NOTICE: This correspondence is not a Formal

Interpretation issued pursuant to NFPA Regulations. Any opinion

expressed is the personal opinion of the author and does not necessarily

represent the official position of the NFPA or its Technical Committees.

In addition, this correspondence is neither intended, nor should it be

relied upon, to provide professional consultation or services.



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to