Per NFPA 30 TABLE 16.5.2.1, I am designing a system using Layout "E" for the in-rack. I am wondering if I am supposed to balance the in-rack with the overhead? I have noted that NFPA 30 for schemes A,B, & C sections: 16.6.1.6 Ceiling sprinkler demand shall not be included in the hydraulic calculations for in-rack sprinklers.
16.6.2.6 Ceiling sprinklers for containers that do not exceed 1 gal (3.8 L) capacity shall meet the following requirements: (1) Ceiling sprinklers shall be designed to protect the surrounding occupancy. (2) Ceiling sprinkler water demand shall not be included in the hydraulic calculations for the in-rack sprinkler protection. (3) Water demand at the point of supply shall be calculated separately for in-rack and ceiling sprinklers and shall be based on the greater of the two. 16.6.3.5 Ceiling sprinkler demand shall not be included in the hydraulic calculations for in-rack sprinklers. 16.6.3.6 Water demand at point of supply shall be calculated separately for in-rack and ceiling sprinklers and shall be based on the greater demand. These all call for the overhead NOT to be balanced with the in-rack but nothing is mentioned for scheme "E". Best regards, Joe Burtell, SET, CFPS Burtell Fire Protection Phone: 406.652.7697 Fax: 406.652.7743 Cell: 406.861.4507 Email: j...@burtellfire.com Web Site: http://www.burtellfire.com _______________________________________________ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: supp...@firesprinkler.org To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org (Put the word unsubscribe in the subject field)