In table 16.5.2.1 to the right of the Table there is a category "Layout".  
You'll see A-F referenced.  Those layouts are described in 16.5.1.10 and 
elsewhere.

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of [email protected]
Sent: Tuesday, December 07, 2010 9:50 AM
To: [email protected]
Subject: Re: NFPA 30 Layout E

Where do you even see scheme E in the code?  I see schemes A, B, and C and
then it skips to G, H, and I.  There is a scheme D talked about in the
annex - annex D - but where are schemes E and F?

There is a long list of errata for NFPA 30 but the missing schemes E and F
are not on the list.  I checked my paper copy and the online version and I
can find no scheme E and F description.  The only mention is table
16.5.2.1.

John Hoffman P.E. | Fire Protection Engineer | Facility Engineering
Services, KCP, LLC - Burns & McDonnell Engineering | National Nuclear
Security Administration's Kansas City Plant | Operated by Honeywell FM&T |
2000 E. 95th St | Kansas City, MO  64131 | ph 816-997-7213 |
[email protected]


                                                                                
                                       
  From:       "Joe Burtell" <[email protected]>                              
                                       
                                                                                
                                       
  To:         <[email protected]>                                
                                       
                                                                                
                                       
  Date:       12/06/2010 11:06 AM                                               
                                       
                                                                                
                                       
  Subject:    NFPA 30 Layout E                                                  
                                       
                                                                                
                                       
  Sent by:    [email protected]                          
                                       
                                                                                
                                       





Per NFPA 30 TABLE 16.5.2.1, I am designing a system using Layout "E" for
the
in-rack. I am wondering if I am supposed  to balance the in-rack with the
overhead? I have noted that NFPA 30 for schemes A,B, & C sections:

16.6.1.6 Ceiling sprinkler demand shall not be included in the hydraulic
calculations for in-rack sprinklers.

16.6.2.6 Ceiling sprinklers for containers that do not exceed 1 gal (3.8 L)
capacity shall meet the following requirements:
(1) Ceiling sprinklers shall be designed to protect the surrounding
occupancy.
(2) Ceiling sprinkler water demand shall not be included in the hydraulic
calculations for the in-rack sprinkler protection.
(3) Water demand at the point of supply shall be calculated separately for
in-rack and ceiling sprinklers and shall be based on the greater of the
two.

16.6.3.5 Ceiling sprinkler demand shall not be included in the hydraulic
calculations for in-rack sprinklers.
16.6.3.6 Water demand at point of supply shall be calculated separately for
in-rack and ceiling sprinklers and shall be based on the greater demand.

These all call for the overhead NOT to be balanced with the in-rack but
nothing is mentioned for scheme "E".

Best regards,

Joe Burtell, SET, CFPS
Burtell Fire Protection
Phone: 406.652.7697
Fax: 406.652.7743
Cell: 406.861.4507
Email: [email protected]
Web Site: http://www.burtellfire.com



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to