Rod,

That's interesting. At least the Portland District Office uses it to a
fault (and I do mean fault).

On Wed, Dec 29, 2010 at 10:34 AM, Rod DiBona <[email protected]> wrote:
> Good information Ron. Thank you for the help. The interesting thing is that 
> we do quite a bit of Corp work, most of it design build and we have never 
> been asked to comply or use Specsintact. So if the Corp uses it they use it 
> intermittently or it has never been enforced on any of our specific jobs.
>
> Rod
>
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Ron Greenman
> Sent: Wednesday, December 29, 2010 10:51 AM
> To: [email protected]
> Subject: Re: USACE Velocity
>
> Yes. Specsintact sucks from an organizational basis since it tends to
> put the horse before the cart, that is, the details drive the
> hierarchy rather than starting with applicable codes, then progressing
> to applicable sections, and then to the details of the section. Get
> the Corps to change to a better organized format where non-applicable
> items can be deleted--NO. Unfortunately even though the bid
> solicitation did not include a reference to Specsintact you are
> expected to know the Corps uses this format and meet it. I've watched
> the document compiler at an engineering firm age prematurely trying to
> understand this formatting.
>
> On Wed, Dec 29, 2010 at 9:39 AM, Rod DiBona <[email protected]> wrote:
>> OK. To get back to the original post. I think Gary makes a good point here. 
>> The more experienced and competent contractors are more likely to pick up on 
>> nuances like this and include the cost in their quote. An unintended 
>> consequence here is that with this in a specification you are more likely to 
>> consistently get the "low bid" contractor.
>>
>> In my case this was advertised as a design build project. The standard list 
>> of documents that the design was to comply with for government jobs was 
>> listed including the UFC 3 -600. No reference to which addition, so we 
>> naturally assumed the most current which is by far the most stringent. The 
>> 2009 added galvanized sch 40 and cut groove only for all dry and preaction 
>> systems. We based our proposal on this and were awarded the project. We 
>> submit our specifications with our 60% drawings and the USACE says they want 
>> the specifications to be chosen from their "Specsintact" ...like their 
>> version of "masterspec." In these specifications the velocity is limited to 
>> 20 fps. The UFC does NOT limit velocity that I know of so this creates a 
>> problem. My question was if anyone was familiar with Specsintact for Corp 
>> jobs and if they were able to persuade them to not use the restriction. 
>> Great discussion thanks for the replies.
>>
>>
>> Rod DiBona
>> Rapid Fire
>>
>> -----Original Message-----
>> From: [email protected] 
>> [mailto:[email protected]] On Behalf Of Todd Williams
>> Sent: Wednesday, December 29, 2010 9:48 AM
>> To: [email protected]
>> Subject: Re: USACE Velocity
>>
>> Another reason for simple, clear and precise specs without all of the
>> BS normally in there. There is no reason for a 54 page specification
>> to relocate 20 heads, even from the Feds.
>>
>>
>> At 11:26 AM 12/29/2010, you wrote:
>>>This spec, that has no code basis, is a great reason why "lesser"
>>>contractors end up with these jobs. When you put a job out to public bid and
>>>you have 20 FP contractors bid on it, the winner will almost always be the
>>>one that missed this type of spec. The type of bidder that
>>>does diligence and finds these weird specs and bids accordingly is probably
>>>the FP contractor that the owner would like to see get the job but will
>>>likely end up with the one that 'misses' this type of spec. Thus the saying
>>>"low bidder built this thing"
>>>
>>>If you want big pipe, say so! If you don't want a 1" grid, say so! But, I
>>>gotta say, I don't know how suspending bigger pipe, makes a structure last
>>>longer.
>>>
>>>
>>>Gary Stites
>>>661-213-9379
>>>
>>>www.rlhfp.com
>>>www.sprinklersoft.net
>>>Pandora Station  http://www.pandora.com/?sc=sh43464983213902734
>>>
>>>On Wed, Dec 29, 2010 at 8:13 AM, Ron Greenman <[email protected]> wrote:
>>>
>>> > Do you have a link? I'm being (L)azy today as I'm on (b)reak and it
>>> > (s)nowed. The RG equation is 1b + 1s = 3L
>>> >
>>> > On Wed, Dec 29, 2010 at 8:08 AM,  <[email protected]> wrote:
>>> > > Todd,
>>> > > Nothing is "snuck" in and there is definitely no entrapment.  It is in
>>> > plain
>>> > > English in the spec.  It is the contractor's responsibility to read all
>>> > of
>>> > > the specification and ask for any clarification that he thinks is 
>>> > > needed.
>>> >  A
>>> > > clarification or amendment for one also for all bidders.
>>> > >
>>> > > Quite frankly, it does help to clarify the reasoning, on this forum,
>>> > behind
>>> > > some of the requirements.  I like open discussions such as these.
>>> >  However,
>>> > > always remember that the spec is a contract document regardless of what
>>> > it
>>> > > requires no matter how ridiculous it may seem.  Everybody bids the same
>>> > set
>>> > > of contract documents.
>>> > >
>>> > > By the way, Hazen-Williams is not all some believe it is.  It works
>>> > fairly
>>> > > well with water based sprinkler systems as long as it is applied
>>> > correctly.
>>> > >  New sprinkler systems with reasonable flows, pressures, velocities, and
>>> > > temperatures will do OK with H-W.
>>> > >
>>> > > One example is working with aged versus new pipe. There is no clear cut
>>> > > methodology to compensate for the added roughage other than lowering the
>>> > > C-factor.  Once you try to get below C=100 you are in no man's land.  I
>>> > > suggest that everyone reads the original works of H&W and see for
>>> > > themselves.  It is free on Google Books as the copyright has expired.
>>> > >
>>> > >
>>> > >
>>> > > Rahe Loftin
>>> > > Sent from my Blackberry
>>> > >
>>> > >
>>> > > ----- Original Message -----
>>> > > From: Todd Williams [[email protected]]
>>> > > Sent: 12/29/2010 10:39 AM EST
>>> > > To: [email protected]
>>> > > Subject: RE: USACE Velocity
>>> > >
>>> > >
>>> > >
>>> > > If you want a safety factor in the design include ONE plainly stated
>>> > safety
>>> > > factor and be done with it. They all typically accomplish the same 
>>> > > thing,
>>> > so
>>> > > keep it simple. Unless you are trying to trip up contractors in the
>>> > bidding
>>> > > process to keep the prices down, there is no reason to do sneak all of
>>> > this
>>> > > little stuff in a spec.
>>> > >
>>> > > At 09:57 AM 12/29/2010, you wrote:
>>> > >>
>>> > >> One last thing to note about the velocity restrictions: their use helps
>>> > to
>>> > >> continue the myth throughout engineering circles that they are a
>>> > necessity.
>>> > >>  I am certain most engineers who see a GSA spec with the velocity
>>> > >> restrictions aren't thinking it is there merely to give a larger safety
>>> > >> factor. Instead they are thinking things like :'high velocity is bad 
>>> > >> for
>>> > >> pipes'; 'it is too noisy'; 'the H-W equation is invalid at high
>>> > velocities',
>>> > >> etc. So they continue to keep it within THEIR specs, which are seen by
>>> > other
>>> > >> engineers and AHJs - and the myths of velocity restrictions continue.
>>> > >>
>>> > >> And if there is a desire to keep the restrictions in place strictly for
>>> > >> the more robust design, then please explain it in the specs, so the
>>> > myths
>>> > >> aren't promulgated. 'As an additional safety factor, all pipe 
>>> > >> velocities
>>> > >> shall be limited...' At least then if the design goes awry the
>>> > >> designer/engineer can come back and explain why the restriction should
>>> > be
>>> > >> lifted for their particular case.
>>> > >>
>>> > >> Mark A. Sornsin, PE | Fire Protection Engineer
>>> > >> Ulteig Engineers, Inc. |Fargo, ND
>>> > >> Direct:    701. 280.8591 | www.ulteig.com
>>> > >>
>>> > >> -----Original Message-----
>>> > >> From: [email protected]
>>> > >> [mailto:[email protected]] On Behalf Of Ron
>>> > Greenman
>>> > >> Sent: Tuesday, December 28, 2010 5:40 PM
>>> > >> To: [email protected]
>>> > >> Subject: Re: USACE Velocity
>>> > >>
>>> > >> Given your argument maybe the oversized main/velocity restriction is
>>> > >> just a simpler way to get desired results in most cases but your
>>> > >> example points to the less than most cases and is valid. And maybe a
>>> > >> simple way to beat the devil isn't any more warranted than designing
>>> > >> to the extreme least costly. Comes back to the fact that some projects
>>> > >> are less critical than others and lend themselves to the low bid at
>>> > >> any cost philosophy, some have higher goals that can be dealt with by
>>> > >> using rule of thumb requirements, and some are so high value that
>>> > >> neither approach works, but since each project is unique until
>>> > >> defined. Each has to be analyzed and assessed, the cost of that
>>> > >> assessment being commensurate with the benefit of paying for it.Mark's
>>> > >> example requires a lot of value engineering to avoid very high
>>> > >> unnecessary costs, a strip mall or the latest Meth Lab Manor apartment
>>> > >> complex needs to be low-balled, while most projects may be somewhere
>>> > >> in between.
>>> > >>
>>> > >> _______________________________________________
>>> > >> Sprinklerforum mailing list
>>> > >> [email protected]
>>> > >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>> > >>
>>> > >> For Technical Assistance, send an email to: [email protected]
>>> > >>
>>> > >> To Unsubscribe, send an email
>>> >
>>> to:[email protected]<to%[email protected]>
>>> > >> (Put the word unsubscribe in the subject field)
>>> > >
>>> > > Todd G. Williams, PE
>>> > > Fire Protection Design/Consulting
>>> > > Stonington, CT
>>> > > 860.535.2080
>>> > > www.fpdc.com
>>> > >
>>> > > _______________________________________________
>>> > > Sprinklerforum mailing list
>>> > > [email protected]
>>> > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>> > >
>>> > > For Technical Assistance, send an email to: [email protected]
>>> > >
>>> > > To Unsubscribe, send an email
>>> >
>>> to:[email protected]<to%[email protected]>
>>> > > (Put the word unsubscribe in the subject field)
>>> > > _______________________________________________
>>> > > Sprinklerforum mailing list
>>> > > [email protected]
>>> > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>> > >
>>> > > For Technical Assistance, send an email to: [email protected]
>>> > >
>>> > > To Unsubscribe, send an email
>>> >
>>> to:[email protected]<to%[email protected]>
>>> > > (Put the word unsubscribe in the subject field)
>>> > >
>>> >
>>> >
>>> >
>>> > --
>>> > Ron Greenman
>>> > Instructor
>>> > Fire Protection Engineering Technology
>>> > Bates Technical College
>>> > 1101 So. Yakima Ave.
>>> > Tacoma, WA 98405
>>> >
>>> > [email protected]
>>> >
>>> > http://www.bates.ctc.edu/fireprotection/
>>> >
>>> > 253.680.7346
>>> > 253.576.9700 (cell)
>>> >
>>> > Member:
>>> > AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC
>>> >
>>> > They are happy men whose natures sort with their vocations. -Francis
>>> > Bacon, essayist, philosopher, and statesman (1561-1626)
>>> > _______________________________________________
>>> > Sprinklerforum mailing list
>>> > [email protected]
>>> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>> >
>>> > For Technical Assistance, send an email to: [email protected]
>>> >
>>> > To Unsubscribe, send an email
>>> to:[email protected]<to%[email protected]>
>>> > (Put the word unsubscribe in the subject field)
>>> >
>>>
>>>
>>>
>>>--
>>>Gary Stites
>>>661-213-9379
>>>
>>>www.rlhfp.com
>>>https://sites.google.com/site/nbcjudah/
>>>https://sites.google.com/site/moondogscc/
>>>www.sprinklersoft.net
>>>Pandora Station  http://www.pandora.com/?sc=sh43464983213902734
>>>_______________________________________________
>>>Sprinklerforum mailing list
>>>[email protected]
>>>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>
>>>For Technical Assistance, send an email to: [email protected]
>>>
>>>To Unsubscribe, send an email to:[email protected]
>>>(Put the word unsubscribe in the subject field)
>>
>> Todd G. Williams, PE
>> Fire Protection Design/Consulting
>> Stonington, CT
>> 860.535.2080
>> www.fpdc.com
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>
>
>
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering Technology
> Bates Technical College
> 1101 So. Yakima Ave.
> Tacoma, WA 98405
>
> [email protected]
>
> http://www.bates.ctc.edu/fireprotection/
>
> 253.680.7346
> 253.576.9700 (cell)
>
> Member:
> AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC
>
> They are happy men whose natures sort with their vocations. -Francis
> Bacon, essayist, philosopher, and statesman (1561-1626)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to