Since the water is for a cooling tower is it treated (chlorinated)?
That would take care of the MIC. Particulates too small to strain
should not be a concern. I presume the cooling tower pumps are PD. If
the filters work for them then that water also supplying a centrifugal
should be no problem. Settling could be mitigated by filling from
after the tower filters. This didn't sound like a tri-water system(s),
but merely stand alone sprinkler systems that were either filled once
and left stagnant or were flowing.

On Wed, Dec 29, 2010 at 9:50 AM,  <[email protected]> wrote:
> Got a project in South America, poor to no municipal infrastructure for water 
> to serve the fire pump.  Owner has issues with spending money for a tank and 
> wants to use the cooling tower basin as the fire pump water source.  The 
> total capacity required is 675,000 gallons and the big issue is airborne 
> contaminants that will find their way in the open basin.  The cooling water 
> systems will use filtration units to separate the contaminants but I've got 
> issue with this water being used for fire protection systems.  Strainers will 
> not work, not fine enough to capture the particulate.  The water coming in to 
> the basin isn't considered potable by our standards.
>
> My major concerns are MIC and clogging of sprinkler heads when this stuff 
> settles.  We have a mix of Office wet pipe systems as well as outdoor exposed 
> dry pipe systems up to 100 ft in height.
>
> The problem with filtration may be the 3,750 gpm flow rate and the pressure 
> drop through the system on the suction side of the pump.
>
> Any thoughts, suggestions?
>
> My initial inclination is to reject the concept.  The cost of the filtration 
> system would probably be close or more than an above ground storage tank.
>
> Craig L. Prahl, CET
> Fire Protection
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> CH2MHILL Extension  74102
> [email protected]
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to