Yeah but where does it state that? NFPA #13R doesn't require sprinklers in 
bathrooms under 55 sq. ft. Ch 6.9 (2007 ed) when talking about bathrooms, 
doesn't say "within dwelling units" as it does with 6.9.3 for the sprinkling of 
closets, pantries etc.

The distinction, as far as I can tell, of"within" and "outside" the dwelling 
units only applies to design criteria and not location - otherwise concealed 
combustible spaces outside the dwelling unit would have to sprinkled which is 
obviously not the case.




      