If you are outside the dwelling unit, it reverts back to NFPA 13. Chapter 8.

Sent from my iPhone
G Tim Stone


On Feb 11, 2011, at 3:01 PM, Ralphy Henderson <[email protected]> wrote:

> Yeah but where does it state that? NFPA #13R doesn't require sprinklers in 
> bathrooms under 55 sq. ft. Ch 6.9 (2007 ed) when talking about bathrooms, 
> doesn't say "within dwelling units" as it does with 6.9.3 for the sprinkling 
> of closets, pantries etc.
> 
> The distinction, as far as I can tell, of"within" and "outside" the dwelling 
> units only applies to design criteria and not location - otherwise concealed 
> combustible spaces outside the dwelling unit would have to sprinkled which is 
> obviously not the case.
> 
> 
> 
> 
> 