I disagree with your assumption that you only add the in-rack demand when the arrangement without excessive clearance would otherwise call for in-rack sprinklers. The supplemental in-racks are offsetting the clearance operating simultaneously with the ceiling sprinkler. Having said that 12.1.3.4 is SLIENT on this issue. Call that an OOPS. I will pursue it at the ROC stage.

As for Class IV exceeding Group A plastic, it happens. The Class IV criteria is judgement driven with minimal testing behind it so a strong dose of conservatism was warranted. Group A plastics have had a ton of tests and when the same storage arrangement for Group A has a lower demand than Class IV, you can apply the Group A criteria (see 16.1.2.2)

Roland

On Feb 17, 2011, at 7:13 AM, Bill Brooks wrote:

Me too until the 2010 language. Now it appears a single row of in- racks can
be used to make up for the excess ceiling clearance requirements for
Chapters 16 and 17. With this set of in-racks in place the racks can be calculated at the actual storage height rather than the theoretical Ceiling - 20 Chapter 16 (or Ceiling - 10 Chapter 17) height required by 13-2007.

The way I read this is the "ceiling clearance in-rack" flow does not have to be added to ceiling flow if the commodity class and "assumed acceptable clearance" would not otherwise require in-racks. When the actual storage height would necessitate the in-racks, then the in-racks could serve double duty as the required in-racks as well as the "ceiling clearance in- racks".
In this case the in-rack flow is added.

All this being stated, my concern is whether this approach is OK for the
Chapter 17 plastics.

Bill Brooks

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to