Clean rooms are an example of where interstitial spaces need sprinklers. I believe this info is found in NFPA 318. Otherwise, a non-combustible concealed space (interstitial space) does not require sprinklers per NFPA 13. Look at section 8.15.1 (2010 ed.) which addresses concealed spaces requiring sprinklers..
Bob Knight -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Todd Williams Sent: Monday, March 07, 2011 11:52 AM To: [email protected] Subject: Re: Interstitial Space Interstitial and concealed can be assumed synonymous in our situation. Interstitial tends to apply more to things like spaces between walls. At 01:46 PM 3/7/2011, you wrote: >Is the space combustible? >On Mar 7, 2011 12:39 PM, "Martin, Matthew" ><[email protected]> >wrote: > > Can anyone tell me what the NFPA says about the requirements of > > sprinklers >in the interstitial space. What is the definition of " Interstitial Space"? > > Also where in the NFPA is the term Interstitial Space used. > > We have an Architect who says that a fully sprinklered building > > includes >sprinklers in all the interstitial spaces. > > > > Thanks in advance, > > > > > > > > Matthew Martin > > CQC Manager > > Suffolk Construction Company, Inc. > > Direct: 323-781-1778 > > Cell: 949-892-7419 > > > > www.suffolkconstruction.com > > > > Please consider the environment before printing this e-mail > > _______________________________________________ > > Sprinklerforum mailing list > > [email protected] > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > > > For Technical Assistance, send an email to: > > [email protected] > > > > To Unsubscribe, send an email > > to:[email protected] > > (Put the word unsubscribe in the subject field) >_______________________________________________ >Sprinklerforum mailing list >[email protected] >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > >For Technical Assistance, send an email to: [email protected] > >To Unsubscribe, send an email >to:[email protected] >(Put the word unsubscribe in the subject field) Todd G. Williams, PE Fire Protection Design/Consulting Stonington, CT 860.535.2080 www.fpdc.com _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)