In the 1980 edition of 13, there was an issue brought up about the sprinklering 
of interstitial spaces.  The answer to that inquiry has been carried forward at 
least to the 1999 edition (regulatory edition for health care occupancies).  
The "intent statement" from NFPA was, 
 
Q:  Is it the intent of 5-1.1 of NFPA 13 that sprinkler protection of the 
interstitial space described above be provided to consider the building 
completely protected by automatic sprinklers?
 
A:  The space described is essentially non-combustible with no occupancy and no 
combustible services [with the possible exception of the cable trays which 
could be protected in accordance with 5-5.1.3 if necessary] and so could be 
treated as a non-combustible concealed space. Use of the space for storage or 
the introduction of combustibles would require provision of sprinklers to 
maintain classification as completely protected by automatic sprinklers.
Issue Edition: 1980
Reference: 3-10.3, 4-1"

Interstitial Spaces are not defined anywhere in the code but there are some 
near misses.  Interstitial is equated with annular.  
 
NFPA 301 (deals with Merchant Vessels - equivalent of 101) uses the phrase, 
"All interstitial spaces (between ceiling and deck above) shall..." but it is 
not included in the Definitions chapter anythwere.  
 
NFPA 96 (Commercial Cooking...) uses the phrase, " ...horizontal duct run in 
the false ceiling (interstitial) space. ..." but does not include it in the 
Definitions chapter except as a term when describing Concealed Space".  
 
7-10.19.3 of the 99 Ed of 13 (Regulatory for  Health Care) provides a measure 
of when to install sprinklers above a clean room -  "Special Occupancy Hazards".
 
Hope that helps.  
 
 
 
 
Tom
 
Tom Scheidel, COO
CMS Survey & Enforcement Process and Life Safety Code
Scheidel & Associates
817-456-6238 
[email protected] 
www.CMS911.com   

Person Centered and Quality Driven!


--- On Mon, 3/7/11, Brown, Mike <[email protected]> wrote:


From: Brown, Mike <[email protected]>
Subject: RE: Interstitial Space
To: "[email protected]" <[email protected]>
Date: Monday, March 7, 2011, 12:42 PM


I'm working a job now that has an interstitial space and we are not putting 
heads in the interstitial space. And the architect is still considering the 
building fully sprinklered.

Mike Brown
Project Designer
Sunland Fire Protection, Inc. 
1218 Elon Place 
High Point, NC 27263
[email protected]   
Business:  336-886-7027 Ext. #140
Fax:  336-886-7024
   

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Martin, Matthew
Sent: Monday, March 07, 2011 1:39 PM
To: [email protected]
Subject: Interstitial Space 

   Can anyone tell me what the NFPA says about the requirements of sprinklers 
in the interstitial space. What is the definition of " Interstitial Space"?
Also where in the NFPA is the term Interstitial Space used.
We have an Architect who says that a fully sprinklered building includes 
sprinklers in all the interstitial spaces.

Thanks in advance,



Matthew Martin
CQC Manager
Suffolk Construction Company, Inc.
Direct: 323-781-1778
Cell: 949-892-7419

www.suffolkconstruction.com

Please consider the environment before printing this e-mail
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to