While true that NFPA 45 requires standpipes for lab buildings 2 stories or 
greater, not ALL lab buildings are required to follow NFPA 45.

Jack Fairchild

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Johnson, Duane 
(NIH/OD/ORS) [C]
Sent: Thursday, March 24, 2011 10:23 AM
To: '[email protected]'
Subject: RE: Standpipes

There is more to it than just IBC...ie. all lab buildings 2 stories or more 
require standpipes per NFPA 45...look at NFPA 101 also...it is combination 
between building construction and an occupancy driven requirement.

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Support Contractor)
Office of Research Services 
National Institutes of Health 
301-496-0487

"Protecting Science - One Sprinkler at a Time"


-----Original Message-----
From: Morey, Mike [mailto:[email protected]] 
Sent: Thursday, March 24, 2011 10:05 AM
To: [email protected]
Subject: RE: Standpipes

For what it's worth, buildings that extend more than 30' below the highest 
level of fire department access also require them (ussually underground parking 
structures trigger this part of the requirement, it's outlined in IFC 905.3:
 
905.3.1 Height. Class III standpipe systems shall be installed throughout 
buildings where the floor level of the highest story is located more than 30 
feet (9144 mm) above the lowest level of the fire department vehicle access, or 
where the floor level of the lowest story is located more than 30 feet (9144 
mm) below the highest level of fire department vehicle access. 

R-3 occupancies are given an exception also
 
Mike Morey, SET
Sprinkler Designer
BMW Constructors, Inc.
O: 317.651.0596 | C: 317.439.2695
www.bmwc.com 
<https://owa.bmwc.com/exchweb/bin/redir.asp?URL=http://www.bmwc.com> 
 

________________________________

From: [email protected] on behalf of Brian Harris
Sent: Thu 3/24/2011 10:00 AM
To: [email protected]
Subject: RE: Standpipes



Jaber-
Thanks!

Brian Harris
FDFP Inc.


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Haji, Jaber M
Sent: Thursday, March 24, 2011 9:55 AM
To: [email protected]
Subject: Re: Standpipes

When the BLDG height exceeds 9 M.


Jaber M. Alhaji
S.Aramco
KSA

On ???/???/????, at ?:?? ?, "Brian Harris" <[email protected]> wrote:

> I don't do enough standpipes to remember a whole lot about their
> requirements, but in a nut shell is it building height that mostly dictates
> when they are needed or is more of the AHJ?
>
>
>
> Brian Harris
>
> First Defense Fire Protection
>
> 11957 Ramah Church Road
>
> Huntersville, NC 28078
>
> Phone: 704.948.3506
>
> Fax: 704.948.3507
>
> Nicet # 128476
>
>
>
>
>
>
>
> =======
> Email scanned by PC Tools - No viruses or spyware found.
> (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.17080)
> http://www.pctools.com/
> =======
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)

The contents of this email, including all related responses, files and 
attachments transmitted with it (collectively referred to as "this Email"), are 
intended solely for the use of the individual/entity to whom/which they are 
addressed, and may contain confidential and/or legally privileged information. 
This Email may not be disclosed or forwarded to anyone else without 
authorization from the originator of this Email. If you have received this 
Email in error, please notify the sender immediately and delete all copies from 
your system. Please note that the views or opinions presented in this Email are 
those of the author and may not necessarily represent those of Saudi Aramco. 
The recipient should check this Email and any attachments for the presence of 
any viruses. Saudi Aramco accepts no liability for any damage caused by any 
virus/error transmitted by this Email.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)



=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.17080)
http://www.pctools.com/
=======





=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.17080)
http://www.pctools.com/
=======
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field) 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to