To this day Scottsdale requires 2.5" valves in stairs or inside one story 
buildings over 10,000 sqft. The rationale was explained to me some time ago but 
it was like "Hose valves are required within 200 ft of all parts of building 
(NFPA #14) so if there is no standpipe then all parts of the building must be 
with 200 ft. of fire truck access. If not 2.5" hose valves are required inside 
the building."


Ron Fletcher
Aero Automatic
Phoenix, AZ




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Thom
Sent: Thursday, March 24, 2011 11:20 AM
To: [email protected]
Subject: RE: Standpipes & NFPA 45

Ron: You exactly right! The AHJ's whom are always right? Use this in very
strange ways. Had one job you could literal drive the engine around the
building and always be a min of 20' maximum of 50' from a 2 story
residential building with all the required Hydrants, stairs and sprinklered,
but still had to put in a horz. Standpipe to the mid landings between the
first and second floor. Still pisses me off. But the owner paid and said not
to fight it, so what ya gonna do?

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ronl.Fletcher
Sent: Thursday, March 24, 2011 12:12 PM
To: [email protected]
Subject: RE: Standpipes & NFPA 45

Thom,

I have seen a lot of AHJ's twist the requirements but I don't believe there
is a prescriptive interior standpipe trade off for required exterior fire
lanes and hydrants.

Ron Fletcher
Aero Automatic
Phoenix, AZ




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Thom
Sent: Thursday, March 24, 2011 10:58 AM
To: [email protected]
Subject: RE: Standpipes & NFPA 45

The other part of IBC/IFC is access to the building. Per IFC trucks have to
be able to reach all sides of the building. I forget the specific
measurement, but I think its within 130FT. or all exterior points of the
building. Horz. Standpipes for even single story if you can't meet it.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Johnson,
Duane (NIH/OD/ORS) [C]
Sent: Thursday, March 24, 2011 8:57 AM
To: [email protected]
Subject: RE: Standpipes & NFPA 45

Agreed. Per NFPA 101: Laboratories using chemicals = NFPA 45.  Laboratories
in healthcare = NFPA 99.  And other labs such as laser labs or sounds labs
will follow other standards.

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Support Contractor)
Office of Research Services 
National Institutes of Health 
301-496-0487

"Protecting Science - One Sprinkler at a Time"


-----Original Message-----
From: Fairchild, Jack [mailto:[email protected]] 
Sent: Thursday, March 24, 2011 10:53 AM
To: [email protected]
Subject: RE: Standpipes & NFPA 45

While true that NFPA 45 requires standpipes for lab buildings 2 stories or
greater, not ALL lab buildings are required to follow NFPA 45.

Jack Fairchild

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Johnson,
Duane (NIH/OD/ORS) [C]
Sent: Thursday, March 24, 2011 10:23 AM
To: '[email protected]'
Subject: RE: Standpipes

There is more to it than just IBC...ie. all lab buildings 2 stories or more
require standpipes per NFPA 45...look at NFPA 101 also...it is combination
between building construction and an occupancy driven requirement.

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Support Contractor)
Office of Research Services 
National Institutes of Health 
301-496-0487

"Protecting Science - One Sprinkler at a Time"


-----Original Message-----
From: Morey, Mike [mailto:[email protected]] 
Sent: Thursday, March 24, 2011 10:05 AM
To: [email protected]
Subject: RE: Standpipes

For what it's worth, buildings that extend more than 30' below the highest
level of fire department access also require them (ussually underground
parking structures trigger this part of the requirement, it's outlined in
IFC 905.3:
 
905.3.1 Height. Class III standpipe systems shall be installed throughout
buildings where the floor level of the highest story is located more than 30
feet (9144 mm) above the lowest level of the fire department vehicle access,
or where the floor level of the lowest story is located more than 30 feet
(9144 mm) below the highest level of fire department vehicle access. 

R-3 occupancies are given an exception also
 
Mike Morey, SET
Sprinkler Designer
BMW Constructors, Inc.
O: 317.651.0596 | C: 317.439.2695
www.bmwc.com
<https://owa.bmwc.com/exchweb/bin/redir.asp?URL=http://www.bmwc.com> 
 

________________________________

From: [email protected] on behalf of Brian Harris
Sent: Thu 3/24/2011 10:00 AM
To: [email protected]
Subject: RE: Standpipes



Jaber-
Thanks!

Brian Harris
FDFP Inc.


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Haji, Jaber M
Sent: Thursday, March 24, 2011 9:55 AM
To: [email protected]
Subject: Re: Standpipes

When the BLDG height exceeds 9 M.


Jaber M. Alhaji
S.Aramco
KSA

On ???/???/????, at ?:?? ?, "Brian Harris" <[email protected]>
wrote:

> I don't do enough standpipes to remember a whole lot about their
> requirements, but in a nut shell is it building height that mostly
dictates
> when they are needed or is more of the AHJ?
>
>
>
> Brian Harris
>
> First Defense Fire Protection
>
> 11957 Ramah Church Road
>
> Huntersville, NC 28078
>
> Phone: 704.948.3506
>
> Fax: 704.948.3507
>
> Nicet # 128476
>
>
>
>
>
>
>
> =======
> Email scanned by PC Tools - No viruses or spyware found.
> (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.17080)
> http://www.pctools.com/
> =======
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)

The contents of this email, including all related responses, files and
attachments transmitted with it (collectively referred to as "this Email"),
are intended solely for the use of the individual/entity to whom/which they
are addressed, and may contain confidential and/or legally privileged
information. This Email may not be disclosed or forwarded to anyone else
without authorization from the originator of this Email. If you have
received this Email in error, please notify the sender immediately and
delete all copies from your system. Please note that the views or opinions
presented in this Email are those of the author and may not necessarily
represent those of Saudi Aramco. The recipient should check this Email and
any attachments for the presence of any viruses. Saudi Aramco accepts no
liability for any damage caused by any virus/error transmitted by this
Email.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)



=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.17080)
http://www.pctools.com/
=======





=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.17080)
http://www.pctools.com/
=======
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field) 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to