I have a fire marshal wanting me to show him where in NFPA 13 it dictates the minimum and maximum spacing of in-rack sprinklers. This is a good question, for the life of me I have never found it in black and white. I know that there are several references to 8'-0" maximum spacing per sprinkler for storage up to 25'-0" but we are only storing up to 20'-0".
I have always been under the impression that you space a sprinkler in each in-rack flue space, usually on the center point of the rack or at the rack upright. Normally the racks are spaced around 8'-0" O.C. but there is one here that is 4'-0" O.C. We are using intermediate level in-rack sprinklers with the overhead system being ELO sprinklers-no ESFR, Large Drop, etc... We are using NFPA 13, 2002 Edition here in Florida. What says the community ? -- Sean Lockyer Project Designer Delta Fire Sprinklers (407) 328-3000, ext 139 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)
