And see (2002) 8.6.3.4.3 for permission to space less than 6ft. What more does he need to know? Has he never read the Standard?
Craig L. Prahl, CET Fire Protection CH2MHILL Lockwood Greene 1500 International Drive Spartanburg, SCĀ 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 CH2MHILL Extension 74102 [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Ed.Tambini Sent: Tuesday, March 29, 2011 3:21 PM To: '[email protected]' Subject: RE: In-rack sprinkler maximum and minimum spacing... If you can use the 2007 edition use 8.13.4.1 for spacing less than 6 feet. Maximum spacing is based on the tables and figures for commodity types and heights -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Sean Lockyer Sent: Tuesday, March 29, 2011 12:14 PM To: [email protected] Subject: In-rack sprinkler maximum and minimum spacing... I have a fire marshal wanting me to show him where in NFPA 13 it dictates the minimum and maximum spacing of in-rack sprinklers. This is a good question, for the life of me I have never found it in black and white. I know that there are several references to 8'-0" maximum spacing per sprinkler for storage up to 25'-0" but we are only storing up to 20'-0". I have always been under the impression that you space a sprinkler in each in-rack flue space, usually on the center point of the rack or at the rack upright. Normally the racks are spaced around 8'-0" O.C. but there is one here that is 4'-0" O.C. We are using intermediate level in-rack sprinklers with the overhead system being ELO sprinklers-no ESFR, Large Drop, etc... We are using NFPA 13, 2002 Edition here in Florida. What says the community ? -- Sean Lockyer Project Designer Delta Fire Sprinklers (407) 328-3000, ext 139 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)