Note that there is nothing about accessibility, occupiability or
storage in this NFPA 96 definition.

On Tue, Mar 29, 2011 at 3:12 PM, Barry Clarke <[email protected]> wrote:
> NFPA does publish a "Glossary of Terms" and has a listing for concealed
> space taken from NFPA 96.
>
> "That portion of a building behind walls, over suspended ceilings, in pipe
> chases, attics, and in whose size might normally range from 1" stud spaces
> to 8 ft interstitial truss spaces and that might contain combustible
> materials such as building structural members, thermal and/or electrical
> insulation, and ducting."
>
>
> Barry Clarke
> Summerland, B.C.
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Matthew J.
> Willis
> Sent: March 29, 2011 2:38 PM
> To: [email protected]
> Subject: RE: concealed space definition
>
> And as you were just shown in your example that is not a viable solution. I
> like simple. Searching thru the 1.2million other codes/standards for a
> definition that may or may not work based on context takes up too much day.
>
> R/
> Matt
>
>
>
>
>
> Matthew J. Willis
> Automatic Fire Sprinklers
> Norred Fire Systems L.L.C.
> 318-387-1134 Voice
> 318-816-1087 Mobile
> 318-387-1163 Facsimile
> [email protected]
>
>> >-----Original Message-----
>> >From: [email protected] [mailto:sprinklerforum-
>> >[email protected]] On Behalf Of Brad Casterline
>> >Sent: Tuesday, March 29, 2011 4:30 PM
>> >To: [email protected]
>> >Subject: RE: concealed space definition
>> >
>> >Matt,
>> >
>> >If there are any other NFPA codes with definitions, I use those first. A
>> >good example for ceilings is NFPA 72-- It tells how to figure the slope
>> >of
>> >curved ceilings.
>> >
>> >-----Original Message-----
>> >From: Matthew J. Willis [mailto:[email protected]]
>> >Sent: Tuesday, March 29, 2011 4:24 PM
>> >To: [email protected]
>> >Subject: RE: concealed space definition
>> >
>> >He asked for a Formal Definition. NFPA 13 does not have one. Chapter 3
>> >tells
>> >us to use Merriam-Webster's Collegiate Dictionary, 11th edition (3.1)
>> >So from Merriam Webster Online:
>> >
>> >conceal
>> >: to place out of sight <concealed himself behind the door>
>> >
>> >space:
>> >a : a limited extent in one, two, or three dimensions : distance, area,
>> >volume
>> >
>> >R/
>> >Matt
>> >
>> >Matthew J. Willis
>> >Automatic Fire Sprinklers
>> >Norred Fire Systems L.L.C.
>> >318-387-1134 Voice
>> >318-816-1087 Mobile
>> >318-387-1163 Facsimile
>> >[email protected]
>> >
>> >> >-----Original Message-----
>> >> >From: [email protected] [mailto:sprinklerforum-
>> >> >[email protected]] On Behalf Of Brad Casterline
>> >> >Sent: Tuesday, March 29, 2011 4:16 PM
>> >> >To: [email protected]
>> >> >Subject: RE: concealed space definition
>> >> >
>> >> >You bet-- there was a quite a bit here recently about it-- wasn't an
>> >Arch
>> >> >trying to symantic his a$$?
>> >> >
>> >> >-----Original Message-----
>> >> >From: [email protected] [mailto:[email protected]]
>> >> >Sent: Tuesday, March 29, 2011 4:04 PM
>> >> >To: [email protected]
>> >> >Subject: RE: concealed space definition
>> >> >
>> >> >No, that's not always the case as there are several references within
>> >> >NFPA
>> >> >13 dealing with a concealed space that has limited access.   So the
>> >space
>> >> >may have access and still be a concealed space.
>> >> >
>> >> >Typically a concealed space is one that does not permit occupancy or
>> >> >storage, has limited or no access, and whose area is not readily
>> >viewable
>> >> >from the occupied space.
>> >> >
>> >> >Craig L. Prahl, CET
>> >> >Fire Protection
>> >> >CH2MHILL
>> >> >Lockwood Greene
>> >> >1500 International Drive
>> >> >Spartanburg, SC  29304-0491
>> >> >Direct - 864.599.4102
>> >> >Fax - 864.599.8439
>> >> >CH2MHILL Extension  74102
>> >> >[email protected]
>> >> >
>> >> >
>> >> >
>> >> >-----Original Message-----
>> >> >From: [email protected]
>> >> >[mailto:[email protected]] On Behalf Of Brad
>> >> >Casterline
>> >> >Sent: Tuesday, March 29, 2011 4:05 PM
>> >> >To: [email protected]
>> >> >Subject: RE: concealed space definition
>> >> >
>> >> >Concealed:
>> >> >Rendered inaccessible by the structure or finish of the building.
>> >> >
>> >> >NFPA 73-2006 3.3.6
>> >> >
>> >> >-----Original Message-----
>> >> >From: Todd Williams [mailto:[email protected]]
>> >> >Sent: Tuesday, March 29, 2011 2:48 PM
>> >> >To: [email protected]
>> >> >Subject: concealed space definition
>> >> >
>> >> >Is there anywhere in 13 where a concealed space is defined? I have
>> >some
>> >> >idiot architect that is insisting on a formal deinition
>> >> >
>> >> >Todd G. Williams, PE
>> >> >Fire Protection Design/Consulting
>> >> >Stonington, CT
>> >> >860.535.2080
>> >> >www.fpdc.com
>> >> >
>> >> >_______________________________________________
>> >> >Sprinklerforum mailing list
>> >> >[email protected]
>> >> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> >> >
>> >> >For Technical Assistance, send an email to: [email protected]
>> >> >
>> >> >To Unsubscribe, send an email to:Sprinklerforum-
>> >[email protected]
>> >> >(Put the word unsubscribe in the subject field)
>> >> >
>> >> >_______________________________________________
>> >> >Sprinklerforum mailing list
>> >> >[email protected]
>> >> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> >> >
>> >> >For Technical Assistance, send an email to: [email protected]
>> >> >
>> >> >To Unsubscribe, send an email to:Sprinklerforum-
>> >[email protected]
>> >> >(Put the word unsubscribe in the subject field)
>> >> >_______________________________________________
>> >> >Sprinklerforum mailing list
>> >> >[email protected]
>> >> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> >> >
>> >> >For Technical Assistance, send an email to: [email protected]
>> >> >
>> >> >To Unsubscribe, send an email to:Sprinklerforum-
>> >[email protected]
>> >> >(Put the word unsubscribe in the subject field)
>> >> >
>> >> >_______________________________________________
>> >> >Sprinklerforum mailing list
>> >> >[email protected]
>> >> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> >> >
>> >> >For Technical Assistance, send an email to: [email protected]
>> >> >
>> >> >To Unsubscribe, send an email to:Sprinklerforum-
>> >[email protected]
>> >> >(Put the word unsubscribe in the subject field)
>> >> >No virus found in this incoming message.
>> >> >Checked by AVG - www.avg.com
>> >> >Version: 9.0.894 / Virus Database: 271.1.1/3528 - Release Date:
>> >03/29/11
>> >> >01:34:00
>> >
>> >_______________________________________________
>> >Sprinklerforum mailing list
>> >[email protected]
>> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> >
>> >For Technical Assistance, send an email to: [email protected]
>> >
>> >To Unsubscribe, send an email to:[email protected]
>> >(Put the word unsubscribe in the subject field)
>> >
>> >_______________________________________________
>> >Sprinklerforum mailing list
>> >[email protected]
>> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> >
>> >For Technical Assistance, send an email to: [email protected]
>> >
>> >To Unsubscribe, send an email to:[email protected]
>> >(Put the word unsubscribe in the subject field)
>> >No virus found in this incoming message.
>> >Checked by AVG - www.avg.com
>> >Version: 9.0.894 / Virus Database: 271.1.1/3528 - Release Date: 03/29/11
>> >01:34:00
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to