Tom, 13 allows 2 sprinks from a single outlet providing the calcs work
(section 8.15.19.5.3 2007).  If that's the case, you're good to go.

Ed Kramer

> OK, here's one to throw around.
> Looked at a retrofit job last week.
> It's about 15K SF of office area being cut up.  The old overhead grid
> system
> is all done with 5' flexheads off 1/2" outlets with reducer bushings.  I
> asked why they called me.  They need to add more heads, can I do the
> same as
> what's there now?  In some instances, there are 2 flexheads off a single
> 1/2" outlet.  Just for giggles, I ran some quick hydraulics using the
> main
> drain data, 125 S, 110 R.  Seems like what's there will work (even the
> doubles) mostly due to the 2" branchlines between the 4" crossmains.
> Many
> need to be moved, some added, some removed,.. Keep going?
> TD