I'm guessing only having to add 8-10 new heads and the old grid is 10x10,
very old screw pipe, Hodgeman uprights on 2x2x1/2 tees, probably as clean as
a whistle inside (as usual).  The current design is 12x14 for the 2x2
ceiling.  It's funny, I think if they didn't need to add any they probably
would have just done it themselves.  His helper says they usually just do it
themselves but never relieve pressure (!).  I guess why even call the alarm
guy if you don't have to.  

TD
Go Red Sox!


as long as you calc includes the 5 ft eqv length of the BL tee (since  
the sprinkler is not attached to the tee) and that for the flexhead  
(about 10 ft), why not?

Roland