Pressure coming from 60 psi submersible well pump - volume coming from several pressure tanks in series. 10 minutes would be met.
On Mon, Apr 25, 2011 at 12:46 PM, Mike Cabral <[email protected]>wrote: > 2007 13D 5.1.1 "Tanks, expansion tanks, pumps . . . shall not be required > to be > listed. You would however, need to meet the plumbing code requirements for > the > tank. NSF listed if tied into the domestic. Question where is the pressure > and > volume coming from? Will the well pump be able to meet the sprinkler demand > for > the 10 min requirement? > > > > Mike Cabral > Cell 314-412-1800 > E-Fax 636-438-1338 > > > > > ________________________________ > From: IPA <[email protected]> > To: [email protected] > Sent: Mon, April 25, 2011 12:35:44 PM > Subject: 13D Pressure Tanks > > Question about 13D & pressure tanks: > > 1.) I have a 13D system where the owner would like to go with a well and > pressure tank installation for their sprinkler & domestic water. The 13D > Handbook (2007) states that NFPA 13 should be consulted for info regarding > the pressure tanks. Okay, so NFPA #13 says, among other things, that > "Pressure tanks shall not be used to supply other than sprinklers and hand > hose attached to sprinkler piping." Doesn't this rule them out for a > combined domestic/sprinkler application? > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)